    Starting systems hermetic compr



    Does someone knows a good manual, book, pdf, about the different starting systems of compressors: current relay, potential relay, start and run caps, units without current nor potential relay, only a start cap,...

    Especially the starting systems from Unité Hermétique, Tecumseh, Aspera,...

    For example, I have 2 different explanations about potential relays, cut in voltage and holding voltage of these relays,..


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Starting systems hermetic compr

    There are many type of starting: CSIR (capacitor start, induction run), CSR (capacitor start and run), CSCR (capacitor start, capacitor run).
    Induction run uses amperometric relay, capacitor run uses voltmetric relay.
    By using the above acronyms and terminology, there are different pages on the internet explaining the various starting methods.
    I have some documents, but they are copyrighted material I used for trainings.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Starting systems hermetic compr

    It was mainly the PSC starting method which bothers me most.
    I would like to explain this starting-up from the magnetic field in the compressor why you need a start winding, why the motor doesn't know how to start when energizing,...
    I would like to see how others approach this, starting from zero.
    Knowing how something works is good but be able to explain this this easily is even better.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Starting systems hermetic compr

    This is a good one but this explanation isn't starting from the beginning.
    http://nanskill.go.th/air/data/Compr...art-Relays.pdf
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Starting systems hermetic compr

    Perhaps others can benefit from my search, from page 199 till 217 http://www.scribd.com/doc/7268693/El...for-HVAC-Techs
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Starting systems hermetic compr

    Potential relay,

    Some say that the voltage over the potential relay coil will be 70% of the connected line voltage, some say that the generated voltage will add up to the line voltage.

    Copy/paste from http://www.exchangor.com/csr_motor.shtml


    # The operation of the potential starting relay is based on the increase in back electromotive force (back EMF) or a bucking voltage that is generated across the start winding as the motor increases in speed.
    # The large metal mass of the motor's rotor turning at high speeds has a voltage generating effect. This generated back EMF opposes line voltage and can be measured across the start winding or across the coil of the potential relay at terminals 2 and 5.
    # The back EMF is usually a higher voltage than the line voltage and can be in the 400-V range.
    # All motors have different magnitudes of back EMF.
    # The back EMF voltage generated across the start winding causes a small current to flow in the start winding and in the potential relay coil since they are in the same circuit.
    # When the back EMF has built up to a high enough value, referred to as pick-up voltage, the contacts between terminals 1 and 2 will be picked-up opened.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: Starting systems hermetic compr

    Quote Originally Posted by Peter_1 View Post
    Does someone knows a good manual, book, pdf, about the different starting systems of compressors: current relay, potential relay, start and run caps, units without current nor potential relay, only a start cap,...

    Especially the starting systems from Unité Hermétique, Tecumseh, Aspera,...

    For example, I have 2 different explanations about potential relays, cut in voltage and holding voltage of these relays,..


    From college days


    Potential (or Voltage) Operated Relay

    These Relays are used for Capacitor Start / Capacitor Run Motors only. The Relay coil is sensitive
    to Voltage other than current and it is connected in Parallel with the Start Winding of the Motor.

    The Voltage across the Start winding is small at switch on and increases progressively as the speed
    increases to reach a maximum at normal running speed.

    At switch on, current flows from the supply through the Run winding and also from the supply, through
    the Start and Run capacitors, through the Start Winding. When the speed has increased enough, the
    Relay pulls in (ie at its normal, preset, pull in voltage) its contact opens and the Start capacitor is
    disconnected. This allows the Motor to continue to run with current passing directly to the Run Winding
    and via the Run Capacitor, to the Start winding also.


    coolrunnings

    .

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Starting systems hermetic compr

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Starting systems hermetic compr

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Starting systems hermetic compr

    This is more what I was looking after
    http://www.tcf.com/TCFBlower/pdfs/engr_data/ED1100.pdf
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Starting systems hermetic compr

    Hi, Peter. Great PDF. I wonder how to boil all that information down to something I can equip my techs with.

    I read it perhaps too quickly, but I have long puzzled over voltage ratings and didn't see anything about that.

    Also, I am puzzled that the wire thickness is less in a start winding than in the run windings. And I further wonder about hard start kit applications, which to me do not seem to add the capacitor function.

    Good stuff. Well worth rereading. This has long been a puzzlement to me.

  12. #12
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Starting systems hermetic compr

    Hi Peter.

    This is a good book. I keep in the van.
    Attached Images Attached Images

  13. #13
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    193
    Rep Power
    20

    Re: Starting systems hermetic compr

    can ytou scan a couple of pages to show us, or tell us where to get it?

Similar Threads

  1. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  2. Annie A-12 hermetic compr tester
    By Peter_1 in forum Electrical
    Replies: 27
    Last Post: 30-04-2010, 02:50 PM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  4. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •