    split system reach not maintaining temp



    Here we go, i have commercial reach in split system R22 with 4 omni temp evaps (2) OTD-13 and (2)OTD-17 in a custom basecabinet. each evaporator has its own txv with a tstat controlling one solinode valve stopping flow to all evaps.. the line set has been extended to about 100ft from building renovation twice since 2002. The condensing unit (1) is on a rack on the 2nd floor the compressor was replaced recently with a copeland CR18KQ-PFV-980WB The system has asight glass before the drier which was slightly flashing... highside 265 and lowside 65.. subcooling 7degrees I cannot get the reach in temp below 43degrees.. line set is 7/8 and 3/8....



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: split system reach not maintaining temp

    We need to know the temps of the air entering and leaving the evaps and cond, as well as the liquid line temp and the suction line temp at the TXV bulb.

Similar Threads

  1. split system charging
    By frankman in forum Air Conditioning
    Replies: 8
    Last Post: 15-11-2010, 03:24 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. Lost Remote Control for Split System AC
    By kiamaian in forum Air Conditioning
    Replies: 5
    Last Post: 12-04-2009, 06:12 PM
  4. High Liquid Line Temperature
    By airefresco in forum Commercial
    Replies: 37
    Last Post: 11-02-2009, 04:36 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •