    Red face Intermittent flash gas in liquid line help.



    Hello

    Small cold room set point 5c holding at 6.5c

    R22

    Condenser on:26c Off:34c subcooling 6c (measured once only)

    Evaporator on:7c Off: 5c superheat 12c (measured once only in wrong place)

    LP 3.5 bar / -3c
    HP 15 bar / 42c


    Can anyone explain why the sight glass on this job is full for about five minutes, then flashes off by about 50% then slowly fills up again after 5 mins or so?

    I don't want to replace TEV until i'm sure.

    Any ideas anyone?

    Thanks All



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Intermittent flash gas in liquid line help.

    Sounds like the valve is hunting a bit, does the suction pressure go up and down a bit too?

    I have a guide book by danfoss on setting up valves somewhere, but can't find it to check but i suspect it could be the orifice is too big.
    Wait for more knowledgeable members opinions before a trip the wholesalers though

    What was the reason for you attending the cold room?

    Jon

  3. #3
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Intermittent flash gas in liquid line help.

    Called out as room too warm, they want 4 degrees (dairy fridge).

    Is it normal for the sight glass to empty when a valve is hunting or could this also be slightly short of gas?

    Thanks

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Intermittent flash gas in liquid line help.

    Could be that someone has adjusted the TEV out of range.

    Sort fault finding from Sporlan here...
    http://www.sporlanonline.com/Form10-143.pdf (260kb)
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Intermittent flash gas in liquid line help.

    I would add refrigerant until the subcooling is about 8-8.5K, then take new readings.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Intermittent flash gas in liquid line help.

    it's a phenomena where your liquid is leaving your condenser at near 0 SC. On a log p/h graph, your left point on the condensing line is just on the saturated line.

    When it starts flashing cover once fast your condenser with a piece of paper, you will see that the bubbles will disappear. Leave it there for 1 minute and then remove it, the bubbles will com back within 5 seconds.
    Is the fan perhaps HP controlled?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Intermittent flash gas in liquid line help.

    Quote Originally Posted by Gary View Post
    I would add refrigerant until the subcooling is about 8-8.5K, then take new readings.
    How will he do this when there's a receiver? The additional added refrigerant will store in his receiver because the refrigerant it's pushed out at the bottom of the condenser by the HP stream upwards the condenser.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Intermittent flash gas in liquid line help.

    Is it an Unithé Hermétique group?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Intermittent flash gas in liquid line help.

    It's a Unitie Hermetique with no fan speed control

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Intermittent flash gas in liquid line help.

    Typically, A UH has no SC battery in its condenser coil.
    Is your TEV sized not too big
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Intermittent flash gas in liquid line help.

    It would be interesting to measure evap superheat & sight-glass response simultaneously. If they move together, then perhaps TXV hunting could be investigated.

    Could the evap fans be hunting slightly, or even the condenser fan? In other words, something else is causing the system disturbance.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Intermittent flash gas in liquid line help.

    Possibly an undersized liquid line creating the hunting effect.

  13. #13
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Intermittent flash gas in liquid line help.

    Quote Originally Posted by Magoo View Post
    Possibly an undersized liquid line creating the hunting effect.
    An excellent suggestion.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  14. #14
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Intermittent flash gas in liquid line help.

    did they move the external unit for say a half meter and make a bend in the liquid pipe that narrows the pipe diam. someone pushed the pipes aside because the needed the space, ore it looks nicer that way, and reformed the pipes. i can go one for ever like this you now. in 35jr you see some strange things happening that they don't tell you straight away.

    Ice

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Intermittent flash gas in liquid line help.

    Quote Originally Posted by Gary View Post
    I would add refrigerant until the subcooling is about 8-8.5K, then take new readings.

    Quote Originally Posted by Peter_1 View Post
    How will he do this when there's a receiver? The additional added refrigerant will store in his receiver because the refrigerant it's pushed out at the bottom of the condenser by the HP stream upwards the condenser.
    Receiver outlet subcooling.
    Last edited by Gary; 13-09-2010 at 02:41 AM.

  16. #16
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Intermittent flash gas in liquid line help.

    I'm new to this unit but the customer says it's been working fine until now, there have been no recent changes.

  17. #17
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Intermittent flash gas in liquid line help.

    Put a sightglass into liquid line at the TX valve, that will tell you what is entering the TX and creating the hunting effect. Plus re-check the evap superheat conditions. TX valves do go awol

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  3. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 02:29 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •