    Heat load

    Visited today a customer (restaurant) who installed recently a new dining room.
    Dimensions: +/- 12 x 20 x 3,5 m (+/- 36 x 60 x 10 ft)
    Place for 250 sitting persons or 150 while dancing.
    But.... when I entered, temperature was already +/- 40°C on 11 AM.
    But now the clue, the roof is made of a 3 layer polycarbonate plate (with a U value of 2,1 according to the owner)
    The plates are opaque, no other sun protection.

    I did a quick calculation which gave me +/- 115 kW, needed air volume for this +/- 22.000 m³/u or an air change of +/- 25/hour.
    This seems almost impossible..

    Any suggestions or corrections?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Heat load

    Hi peter,

    Iv'e seen on TV its getting hot your way How many AC's do you have at home?

    My suggestion - go away from there, if there is direct radiation of the sun, you can not calculate it.
    Ask the owner to install a proper insulated roof and call you again.

    chemi

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Heat load

    At college they told me the suns energy is increased, radiated plus 80% through a glass roof.........

    So Chemi is spot on...........

    I would not dream of quoting with confidence any area which receives direct sun input through it
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Heat load

    Thanks guys.
    Aiyub, your avatar is gone
    It's indeed very hot but I think these temperatures are rather normal for Chemi in teh Israeli dessert.
    In the shadow, I measured this afternoon 35°C.
    Serviced this afternoon a compressor with a condensor pressure of 28 bar, liquid was +/- 45°C to 50°C.

    That's also what I told the owner already but somebody else gave an offer with a Daikin VRV of 22 kW. I estimated a heat load of 100 kW.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Heat load

    I reckon on about 98.7 kw, I would do the job but insist on blinds for the ceiling and some knid of extract at the highest point to occassionally take away excessive hot air if a pitched roof.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Heat load

    Or they could add a permanent water feature on the roof to provide heat removal !
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    manishjha's Avatar
    manishjha Guest

    Re: Heat load

    please provide easy heat load calculation format in excel sheet.

    Manish Jha

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Heat load

    Rename the restaurant "sauna with foöd " speedo's and bikinis necessary.
    magoo

  9. #9
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21
    Just a couple of ideas in case you are able to lower the calc cooling load:
    a) At the design peak load (afternoon?) are the 150 dancers dancing already, or does that normally occur in the evening (when it is a bit cooler outside)? Ie at peak load in the afternoon, perhaps the customers are normally just seated, eating their lunch.
    b) Are you able to apply some diversity to the customers? Ie is the restaurant always full to capacity at the time of day when the peak cooling load occurs (afternoon?). Maybe it would be sensible (excuse pun) to design on say 75% occupancy (185), or even lower, on the basis that when the place is maxed out (rarely) one would expect the room temp to climb a little outside the design temperature zone.

    You have to discuss ways of reducing the solar heat load, of couse. Solar film can be rather effective and practical (go for the max reduction).

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Heat load

    Original post is already from 2005
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. online heat load calculators
    By pradyumna in forum Tools and Calculators
    Replies: 3
    Last Post: 07-09-2010, 06:42 AM
  2. Calculating heat load
    By Abe in forum Technical Discussions
    Replies: 13
    Last Post: 13-08-2010, 05:40 PM
  3. Heat Load calculation for residential jobs
    By Herschmidt in forum Air Conditioning
    Replies: 2
    Last Post: 12-05-2008, 11:50 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Mortuary heat load
    By smithgmp in forum Commercial
    Replies: 3
    Last Post: 05-05-2003, 04:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •