    R22 to Ammonia
    Can R-22 compressors be used in Ammonia System. If yes do I need to make some changes?
    Dec 2008
    Portugal
    48
    1,020
    Re: R22 to Ammonia
    Yes, If it is an open compressor.
    Change all parts/fittings that have cooper on its own composition. Change gauges, pressure controls.
    Changing seals is also a good idea. Also change the oil and filters. Maybe change the oil 2 times at minimum is a good idea especially if you can use the oil separator so it would be better cleaned.
    Watch out if the same regimen of operating is possible with R717.
    May 2009
    Sydney
    73
    15
    Re: R22 to Ammonia
    Are you just going to use the compressors or are you thinking of retrofitting the whole plant? Also what brand of compressor are you talking about?
    Jul 2009
    India
    Re: R22 to Ammonia
    Quote Originally Posted by gregd1401 View Post
    I am planning to add two Sabroe HF 163 Screw(R 22) compressors in my existing ammonia system.
    Asheesh
    Jul 2009
    India
    Re: R22 to Ammonia
    Quote Originally Posted by Sandro Baptista View Post
    Asheesh
    Dec 2008
    Portugal
    48
    1,020
    Re: R22 to Ammonia
    Check the oil cooler just to be sure. The oil cooler with NH3 for the same regimen needs to release more heat from the oil.
  1. contaminants in ammonia systems
    By Johnny Rod in forum Refrigerants
    Last Post: 17-10-2011, 05:26 PM
  2. Want to be trained as an ammonia operator
    By Randy Williams in forum NH3
    Last Post: 26-11-2008, 08:15 PM
  3. Replies: 21
    Last Post: 03-02-2008, 05:10 PM
  4. Ammonia and CO2 reactor
    By gwapa in forum NH3
    Last Post: 07-01-2007, 04:50 PM
  5. New Ammonia Certification in United States
    By JerrydNH3 in forum NH3
    Last Post: 15-08-2006, 03:10 PM