    capacity fault in frick RXF85H



    hi, we have noticed a drop in capacity in our frick over the last two years . it used to always run at 100% .over the last 2800 hrs it has droped to 96% and we have also noticed that our spiral freaser is not performing aswell as it used to .it used to run at _45deg and now only -34deg.we have had the valve checked manualy and they recon it is wide open.
    any thoughts ?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: capacity fault in frick RXF85H

    mudhog4x4,
    What type of contrller do youhave, is it a frick or other?
    Have you noticed anything else on system like ice thats usually there or not , compressor amp draw or refrigerant levels lower than normal etc .

  3. #3
    mudhog4x4's Avatar
    mudhog4x4 Guest

    Re: capacity fault in frick RXF85H

    hi,i havent noticed any ice or not ,it is a frick controler,and not sure on amps as we dont record them but we do record the fla% and it was always around 82 to 86% and is now around 62%.as for ammonia levels it hides and comes back and in the last two years we have put about 4 bottles in

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: capacity fault in frick RXF85H

    If its a Frick controller you could do a recalibration on slide & slide stop , then see what happens .
    Also is it reaching desired suction set point or is it struggling ?
    If its reaching set point then it won't need to load but you should be able to achieve it manually as a test .

  5. #5
    Join Date
    Sep 2008
    Location
    Newcastle upon tyne
    Age
    75
    Posts
    80
    Rep Power
    16

    Re: capacity fault in frick RXF85H

    Hi

    Can you have evaps with excess oil.

    AWW

Similar Threads

  1. Replies: 3
    Last Post: 29-04-2010, 10:30 AM
  2. How to increase pool heater capacity?
    By Drew in forum Commercial
    Replies: 104
    Last Post: 13-06-2009, 05:25 AM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  4. Frick Quantum LX Compressor control panel: Capacity Control Screen
    By screw_geek in forum Industrial Compressors
    Replies: 17
    Last Post: 15-06-2008, 06:47 AM
  5. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •