Thread: capacity fault in frick RXF85H
-
09-09-2010, 03:48 AM #1
capacity fault in frick RXF85H
hi, we have noticed a drop in capacity in our frick over the last two years . it used to always run at 100% .over the last 2800 hrs it has droped to 96% and we have also noticed that our spiral freaser is not performing aswell as it used to .it used to run at _45deg and now only -34deg.we have had the valve checked manualy and they recon it is wide open.
any thoughts ?
-
09-09-2010, 04:35 AM #2
Re: capacity fault in frick RXF85H
mudhog4x4,
What type of contrller do youhave, is it a frick or other?
Have you noticed anything else on system like ice thats usually there or not , compressor amp draw or refrigerant levels lower than normal etc .
-
09-09-2010, 04:50 AM #3
Re: capacity fault in frick RXF85H
hi,i havent noticed any ice or not ,it is a frick controler,and not sure on amps as we dont record them but we do record the fla% and it was always around 82 to 86% and is now around 62%.as for ammonia levels it hides and comes back and in the last two years we have put about 4 bottles in
-
09-09-2010, 06:11 AM #4
Re: capacity fault in frick RXF85H
If its a Frick controller you could do a recalibration on slide & slide stop , then see what happens .
Also is it reaching desired suction set point or is it struggling ?
If its reaching set point then it won't need to load but you should be able to achieve it manually as a test .
-
12-09-2010, 06:31 PM #5
Re: capacity fault in frick RXF85H
Hi
Can you have evaps with excess oil.
AWW
Similar Threads
-
Heat pump-cooling and heating capacity and capacity of compressor
By sale in forum FundamentalsReplies: 3Last Post: 29-04-2010, 10:30 AM -
How to increase pool heater capacity?
By Drew in forum CommercialReplies: 104Last Post: 13-06-2009, 05:25 AM -
Sensible Heat Factor / capacity of Inverter split Systems at part load?
By Greengrocer in forum Technical SpeculationsReplies: 31Last Post: 09-02-2009, 04:57 PM -
Frick Quantum LX Compressor control panel: Capacity Control Screen
By screw_geek in forum Industrial CompressorsReplies: 17Last Post: 15-06-2008, 06:47 AM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM