    Question Please help me with my project!



    Hi everyone, this is my first post! Im currently working on a small project of mine and need some technical advice. Please forgive me, I am a newb.

    I have a masterflux dc compressor rated for a little over 5000 btu at 30 amps. They sent the compressor with a # 8 fitting on the high side and a #10 on the low side.

    The problem I'm concerned with is that my evaporator and condensor are run in .25 outside diameter line. Will there be any problems with reducing the size down to what I need on the high side and enlarging it up to the low side?

    Also if there arent any problems with that, where should I mought my access ports to get the pressure readings I should rely on?

    Thanks in advance



  2. #2
    Join Date
    Sep 2010
    Location
    United States
    Posts
    8
    Rep Power
    0

    Re: Please help me with my project!

    Also, the compressor is using o-ring fittings but everything I have is flare and I dont have the money to switch it all out. Any problems running an adapter on the compressor fittings? Will that lead to problems in the future?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Please help me with my project!

    Which model compressor is it ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2010
    Location
    United States
    Posts
    8
    Rep Power
    0

    Re: Please help me with my project!

    Sierra 02-0434Y3

  5. #5
    Join Date
    Sep 2010
    Location
    United States
    Posts
    8
    Rep Power
    0

    Re: Please help me with my project!

    anybody out there?

  6. #6
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Please help me with my project!

    Quote Originally Posted by 06isDriver View Post
    Hi everyone, this is my first post! Im currently working on a small project of mine and need some technical advice. Please forgive me, I am a newb.

    I have a masterflux dc compressor rated for a little over 5000 btu at 30 amps. They sent the compressor with a # 8 fitting on the high side and a #10 on the low side.

    The problem I'm concerned with is that my evaporator and condensor are run in .25 outside diameter line. Will there be any problems with reducing the size down to what I need on the high side and enlarging it up to the low side?

    Also if there arent any problems with that, where should I mought my access ports to get the pressure readings I should rely on?

    Thanks in advance
    What does Tecumseh say about it
    My wife used to say you never listen to a word I say at least I think that what she said

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Please help me with my project!

    Sorry but the compressor fittings that you mention don't mean anything to me here in the UK.

    I see, from the spec sheets, that the compressors are supplied with basic copper pipe tails. Are these O-ring fitting brazed onto those tails? If so, can you not remove them so that you connect directly to the copper tail?

    With regard to the access fittings, it depends what pressures you want to measure as to where you put them.

    One each of compressor discharge and suction at least.

    What sort of expansion device are you using to control the system operation?

    anybody out there?
    Please be patient, not everyone is waiting on your every word. The forum covers the world and the many time zones therein.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Sep 2010
    Location
    United States
    Posts
    8
    Rep Power
    0

    Re: Please help me with my project!

    #8 = 13/32" od
    #10 = 1/2" od

    Yes the fittings were brazed on by the reseller. I dont know why they chose #8 and #10 when #6 and #8 would have probably been matched better. I'd rather not cut them off because they were brazed very close to the the compressor housing and I fear i would damage it trying to do that.

    i have a condenser from another 5000 btu system with some sort of coiled expansion tubing already attached. I figured if it worked for it it'll work for mine. No?

    If not how do I size the correct expansion valve?

    Also I understand I'll need a high and low side port, but I was thinking that the pressures could be skewed if i mounted it on a section of larger diameter tube than was actually used throughout the system (.25")

    Also I apologize for seeming impatient. In other forums I am a member of, the thread pace is very fast. I can see this place operates on a slower pace, thats cool.

  9. #9
    Join Date
    Sep 2010
    Location
    United States
    Posts
    8
    Rep Power
    0

    Re: Please help me with my project!

    Tecumseh says talk to Masterflux.

    Masterflux says talk to the technical sheets. The technical sheets dont really tell me what to do in this situation.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Please help me with my project!

    The coiled expansion tubing could be fine. Would suggest fitting a filter drier in the line before the expansion capillary tubing.

    The high and low pressure ports can be fitted to any size pipe the readings will not be affected by the main pipe size.

    Sorry, I'm unable to suggest any solutions to your connectors as I can't see them from here . Does the reseller have any matching connectors to go with those fitted?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Please help me with my project!

    Quote Originally Posted by 06isDriver View Post
    Also I apologize for seeming impatient. In other forums I am a member of, the thread pace is very fast. I can see this place operates on a slower pace, thats cool.
    That's because we all have a regular job and we first have to work before we can play on the computer and help others
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Mar 2007
    Location
    USA
    Posts
    118
    Rep Power
    18

    Re: Please help me with my project!

    Post pix of these fittings we don't seem to be familiar with them

  13. #13
    Join Date
    Sep 2010
    Location
    United States
    Posts
    8
    Rep Power
    0

    Re: Please help me with my project!

    Quote Originally Posted by Peter_1 View Post
    That's because we all have a regular job and we first have to work before we can play on the computer and help others

    I have a regular job too, so you can save your attitude. In fact if it werent for my regular job, you wouldnt even have a computer to "play" on.

    just like if it werent for your regular job, we wouldnt have ac systems to comfort us. It's all relative so dont put yourself on a pedestal.

  14. #14
    Join Date
    Mar 2007
    Location
    USA
    Posts
    118
    Rep Power
    18

    Re: Please help me with my project!

    not for nothing you just dissed a very knowlegable mod

  15. #15
    Join Date
    Sep 2010
    Location
    United States
    Posts
    8
    Rep Power
    0

    Re: Please help me with my project!

    you have to earn respect....and you dont do that by being continually being rude. I apologized once for what some may have seen as impatience.

    I should not and will not tolerate further belittling to accommodate someones ego....mod or not.

  16. #16
    CARSTENSEN's Avatar
    CARSTENSEN Guest

    Re: Please help me with my project!

    You can get mating fittings from Doc' Blocks.


    As for the size of the fittings, these are approproiate for the compressor. Also, the compressors come with and without fittings. The part numbers are different for both.

Similar Threads

  1. how can I raise the pressure for chilled water project
    By mackistired in forum Commercial
    Replies: 4
    Last Post: 17-06-2010, 03:34 AM
  2. Three phase motors (project)
    By zeevalentino in forum Electrical
    Replies: 4
    Last Post: 10-03-2010, 03:16 AM
  3. graduate project help
    By georgeadam20 in forum Fundamentals
    Replies: 3
    Last Post: 24-06-2009, 05:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •