Return Air through Pocket Door Space
Has anyone ever done or even thought of doing a RA utilizing a Pocket Door Space - We could put a RA Frame in the existing wall also. This Frame and space around the door opening itself would be the Grilles for one RA Trunk. It would save a PITA padding out and making an existing room layout ugly.
-
08-09-2010, 02:54 PM #2
Re: Return Air through Pocket Door Space
Supposedly RA is Return Air. Isnt' it?
Now, in order to be able to answer your question we need to know the air flow rate, the external static pressure of the fan for the rated air flow, the size of the door and the gap gauge around the door.
With that, I can calculate the air speed in the gap and the approximate pressure drop.
-
08-09-2010, 06:24 PM #3
Re: Return Air through Pocket Door Space
( :
Yeah and you know it's not an issue ( : With a 36" x 1 3/8" thick door inside a 3 1/2" cavity....
(3 1/2 - 1 3/8") x 36" = 76.5 sq in
Now, if that were actually equal to a 10" dia (it'a a bad aspect ratio), we'd be losing .04 ISP over 100' and the velocity is 459 FPM.
None of this is necessary, by observation everything for flow is cool. I'm wondering if anyone actually does it. ( :
-
10-09-2010, 09:35 PM #4
Re: Return Air through Pocket Door Space
take an inch off the bottom of the door if the flow rate is not too high..
Similar Threads
-
daikin return air problem
By Kev The Tool in forum Air ConditioningReplies: 7Last Post: 17-02-2010, 03:50 PM -
McQuay ALS F XE273.2 990Kw, highest return temp?
By THE WOMBAT in forum Technical SpeculationsReplies: 1Last Post: 07-08-2009, 10:59 AM -
Best place for return air sensors, in the room or ceiling void?
By back2space in forum Air ConditioningReplies: 27Last Post: 06-07-2009, 06:21 AM -
Pressure regular valve for wet return
By hphien in forum IndustrialReplies: 5Last Post: 09-12-2005, 06:28 PM -
return air
By subzero*psia in forum Air ConditioningReplies: 1Last Post: 12-07-2001, 04:02 PM