    Prestcold compressor



    I have a problem with my freezer system.

    Plant record as follows...

    Compressor Delivery Pressure - 13.5bar
    Compressor delivery gas temp - 97c
    Liquid Line temp - 31c
    Product Cooled (Room air) temp - -12c
    Compressor suction - 1bar
    Liquid line sight glass clear and dry. The room temp is meant to come down to -21, but am only achieving -12 to -14. Refrigerant is R417A. Cant find much wrong with it myself, any suggestions?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    It looks like refrigerant is a drop in replacement of R22. If this is the case, did the system achieve -21°C with R22?
    What is the expected capacity against the actual heat load?
    From the discharge gas temperature I see that you probably have a high suction superheat. How much is SSH and suction temperature?

    EDIT: 1 bar suction is -40°C therefore there is definitely something wrong with you evaporating to suction side.
    Last edited by NoNickName; 07-09-2010 at 07:46 PM.

  3. #3
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    The system achieved -21 with R22 and it also used to achieve it with the R417A.

    Can you expand on the question - What is the expected capacity against the actual heat load? -

    Suction temp is 9c. How do i work out suction superheat?

    Do you think there might be something wrong with evaporator?

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    Yes, there is something wrong definitely.
    1 bar(g) corresponds to -25°C saturated liquid.
    The suction temperature is 9°C.
    The suction superheat is 9-(-25)=34K which is way too much.
    The high SSH is a symptom of a starving evaporator.
    I suspect the system is low on gas or the TEV closed or filter drier clogged.

  5. #5
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    What temperature difference would you expect over the filter drier? I have a 6 degree C difference.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    I would expect ZERO. You have a clogged filter.

  7. #7
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    Thats what im thinking, i appreciate your help.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    I would appreciate if you could feed us back after you inspected the drier filter

  9. #9
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    I have one ordered and it is getting flown out on a helicopter on Friday, i will let you know once i have changed it out.

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    Quote Originally Posted by caramelsoul View Post
    I have one ordered and it is getting flown out on a helicopter on Friday, i will let you know once i have changed it out.
    You're on a drilling rig?

  11. #11
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    16

    Re: Prestcold compressor

    Please measure the temperature of the compressor heads as I suspect you have a faulty valve.

  12. #12
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    The temperature on the compressor heads did seem quite high. Are you talking about taking the temperature off the casing over the pistons? One side of it is a lot higher than the other side, 117 degree C and a bit discoloured which i was putting down to heat.

  13. #13
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    Quote Originally Posted by NoNickName View Post
    You're on a drilling rig?
    On an oil production platform.

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    Quote Originally Posted by caramelsoul View Post
    The temperature on the compressor heads did seem quite high. Are you talking about taking the temperature off the casing over the pistons? One side of it is a lot higher than the other side, 117 degree C and a bit discoloured which i was putting down to heat.
    This is normal. One side of the head is the suction, the other side is the discharge. Just like in a car engine, the suction side is colder, the exhaust is warmer.
    The high discharge temperature is in turn caused by the high suction superheat. Once you rectify the SSH, the discharge temperature would also reduce.

  15. #15
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    29
    Rep Power
    0

    Re: Prestcold compressor

    I have used an R22 replacement gas known as MO29 (R422D) and ive found that i need to add 20% extra when charging the system, ive not used 417a but it may be worth checking if this rule applies to this gas as well here is a link to help you
    http://www.gas2010.com/retrofit-hfcs

    cheers

  16. #16
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    Iv changed out the filter drier and there is no difference to the system.

  17. #17
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    Was it dirty or clogged? Have you still got that high temperature drop across it?

  18. #18
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    No, wasnt dirty and still have a slight temp difference of about 4 deg c across it.

  19. #19
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    I still think there is some occlusion somewhere on the liquid line. Was there much oil inside the filter?

  20. #20
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    No, hardly any.

  21. #21
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    TEX problem maybe?

  22. #22
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Prestcold compressor

    i trust its a R22 expansion valve and not R502 or R404A, that would account for the premature shutting down,

    does the suction gauge flutter when fitted,could be valve reeds, R22 makes the heads run hot unless its got the suction valve on the rear case, i would get a head set and have a look if you cant find anything else.

  23. #23
    Join Date
    Aug 2010
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: Prestcold compressor

    It is an R22 expansion valve, but its not prematurely shutting down, its constantly running because its not getting down to desired temp.

    Suction gauge does not flutter.

  24. #24
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Prestcold compressor

    its not going to shut the compressor off but somethings not adding up here, 9deg c suction temps to high and sounds like the TEV is shuting down before the evaps cold enough,try either opening the superheat up a bit or change the valve and check the orafice size.

  25. #25
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Prestcold compressor

    Yeah, I confirm the problem is along the liquid pipe... txv maybe

Similar Threads

  1. copeland scroll durability
    By Third_techtrio in forum Technical Discussions
    Replies: 16
    Last Post: 23-01-2010, 04:47 AM
  2. Catastrophic compressor failure...need info
    By bsh3239 in forum Industrial Compressors
    Replies: 40
    Last Post: 28-11-2009, 04:30 PM
  3. [Autocascade] Only a project ATM
    By before in forum CPU Overclockers
    Replies: 1
    Last Post: 07-05-2009, 11:13 AM
  4. seized inv compressor
    By flash in forum Air Conditioning
    Replies: 2
    Last Post: 09-04-2008, 06:56 PM
  5. Compressor Capacity
    By engrkate in forum Fundamentals
    Replies: 15
    Last Post: 13-10-2006, 12:11 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •