Results 1 to 6 of 6
  1. #1
    Join Date
    Jun 2009
    Location
    greece
    Posts
    11
    Rep Power
    0

    oil pressure switch



    hi everyone.i have a bitzer compresor.it works fine but it cuts off the oil pressure switch...when i reset it it works again fine and after 2 days it cuts off again and the story continues....any ideas?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: oil pressure switch

    If oil level is OK and you don't have oil return problems, then check the oil filter. If it is clean that your next stop is the oil pump.

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: oil pressure switch

    hi stathis, it would take you just 2 mins to test the oil switch< or 120 seconds <

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: oil pressure switch

    If the oil is excessively and occasionally diluted with liquid refrigerant, its viscosity drops and the differential pressure across the pump may fall below the switch threshold. Check suction superheat at all conditions, especially at part load.

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: oil pressure switch

    Is the crank case heater ok and wired correctly?

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: oil pressure switch

    Could also be due to a faulty discharge reed.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. How to Design Refrigeration Systems
    By US Iceman in forum Fundamentals
    Replies: 63
    Last Post: 24-07-2008, 04:27 PM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. Pressure Switch
    By Abe in forum Commercial
    Replies: 1
    Last Post: 23-01-2003, 05:47 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •