    For the chiller guys



    I was looking at an antifrost fault on a MultiClima chiller today. (Just so you know why I had it open)
    I don't get much practice on chillers in general, so wanted to ask a couple of general questions on parts of the fridge circuit itself:

    a) What is the purpose of liquid injection (controlled by a solenoid valve) into the evaporator just after the TEV?

    b) What is the purpose of hot gas 'by-pass' (controlled by a solenoid valve) straight back into the suction line?

    This specific chiller has 2 x 3 cylinder recip compressors, 1 on each circuit; each compressor has 2 unloaders. It has 1 common plate evaporator with normal TEV's.

    While I'm asking, I have also come across a slightly different setup on a Ciat chiller, where they have the discharge line tee off through a capacity valve and also into the evaporator just after the TEV. What's it for?

    Thanks
    Craig


    If at first you DO succeed, try to hide your astonishment!!

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: For the chiller guys

    1) to avoid excessive suction superheat and it's associated high discharge gas temperature from compressor in extremely low part load condition. It is normally actuated by a temperature probe on the discharge pipe and one thermostat set to 100 or 120°C.

    2) If you don't have a condensing control device, and in winter time it can be possible to over-condense or over-subcool, you by pass some hot gas into the suction to reduce the effectiveness of the condenser.

    If it was me, from a design point of view I would put the liquid injection straight into the suction, but a liquid slugging would then be possible.
    Last edited by NoNickName; 08-09-2010 at 07:58 AM.

  3. #3
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: For the chiller guys

    Thanks NoNickname, it's good to understand these additional control features.

    They have the hot gas bypass on VRV systems I work on, but the liquid injection after the TEV is a seldom-used concept for me. I have seen some bespoke remote condensing units with excessive pipe-runs where they use liquid injection to keep the compressor cool, and that would be the same concept then. Reducing the non-useful superheat value so the compressor doesn't overheat.

    Thanks for your time.
    If at first you DO succeed, try to hide your astonishment!!

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: For the chiller guys

    Please add to my reputation points.

  5. #5
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: For the chiller guys

    Quote Originally Posted by NoNickName View Post
    Please add to my reputation points.
    Sure no problem, just let me know how
    If at first you DO succeed, try to hide your astonishment!!

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: For the chiller guys

    Click on the top right corner of the message. There's a scale icon.

  7. #7
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: For the chiller guys

    Multi-clima really are a bag of turd.....dont you think acnerd?

  8. #8
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: For the chiller guys

    Quote Originally Posted by wilko123 View Post
    Multi-clima really are a bag of turd.....dont you think acnerd?
    as long as they do the job wright, there good. any brand that shows allot of the same failures are bags of dirt.

    Ice

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: For the chiller guys

    Quote Originally Posted by acnerd View Post
    While I'm asking, I have also come across a slightly different setup on a Ciat chiller, where they have the discharge line tee off through a capacity valve and also into the evaporator just after the TEV. What's it for?

    Thanks
    Craig
    they are pressure regulators for the evap/plate heat exchanger. it helps getting a steady suction pressure. They also have a slight hot gas by-pass function when the pressure is to high. That is why the evaps are cracking inside diu to thermal shocks, and the water and refrig blend.

    Ice

  10. #10
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: For the chiller guys

    Quote Originally Posted by wilko123 View Post
    Multi-clima really are a bag of turd.....dont you think acnerd?
    Did you rhyme that on purpose, or is it just me.

    First one i have worked on. And I'm not a fan of any chiller that uses belt-driven condensor fans.
    If at first you DO succeed, try to hide your astonishment!!

  11. #11
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: For the chiller guys

    Quote Originally Posted by icecube51 View Post
    . They also have a slight hot gas by-pass function when the pressure is to high. That is why the evaps are cracking inside diu to thermal shocks, and the water and refrig blend.

    Ice
    Thanks Icecube51. When you say the pressure is too high, do you mean the discharge pressure? So for example, the hot ambient even with the fans at full speed, causes it to bleed hot gas into the evaporator to avoid HP cutout?
    If at first you DO succeed, try to hide your astonishment!!

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: For the chiller guys

    Quote Originally Posted by icecube51 View Post
    they are pressure regulators for the evap/plate heat exchanger. it helps getting a steady suction pressure. They also have a slight hot gas by-pass function when the pressure is to high. That is why the evaps are cracking inside diu to thermal shocks, and the water and refrig blend.

    Ice
    On some of the Hussman supermarket systems, warm gas from the top of the receiver is used for defrosting in order to minimize thermal shock in the evaporator. I wonder if this wouldn't work just as well in other systems, thus avoiding evaporator cracking.

  13. #13
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: For the chiller guys

    i have one now whit a cracked plate evaporator. the fault was a continuously manual reset from the owner. by-passing the LP switch is the most stupid thing you can do.
    we have several CIAT chillers in maintenance, and the problems are no different than the other brands.

    Ice

  14. #14
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: For the chiller guys

    Quote Originally Posted by acnerd View Post
    Did you rhyme that on purpose, or is it just me.

    First one i have worked on. And I'm not a fan of any chiller that uses belt-driven condensor fans.

    No but it is kind of catchy!

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Problems in r22 chiller design
    By umeshpradhan in forum Technical Discussions
    Replies: 9
    Last Post: 06-07-2010, 10:39 AM
  3. Chiller operation best practice
    By Emmett in forum Technical Discussions
    Replies: 1
    Last Post: 10-03-2010, 08:23 PM
  4. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •