    Need help!



    hey guys im on site engineer at a call centre no air con tools on site with me,iv got u4 fault on 3 systems the temp dropped from 21 cooling to 16 i no what the fault is but what i dnt no is how to fix it any advice ?



  2. #2
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: Need help!

    iys daikin by the way and they were set on 21 cooling 22 heating

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Need help!

    Communication fault between indoor and outdoor

  4. #4
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: Need help!

    yeh i no the fault how do i fix it?

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Need help!

    Check communication between indoor and outdoor. Check wiring does not go along together with power cables. Switch off and on to try resetting communication.
    If everything else fails, it may be the PCBs have suffered a power surge and the three need to be replaced.

  6. #6
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: Need help!

    nice one fella job done