Results 1 to 13 of 13
Thread: Tonnage to KW
06-09-2010, 08:26 PM #1
Tonnage to KW
This may seem a dumb question but is there as mathematical equation to convert tons of cooling in to kw's i've googled but only found converters and would like to be able to work this out for myself
eg if i had a small chiller unit rated at 95 tonnes what would that equate to in KW'S
thanks
James
06-09-2010, 08:29 PM #2
Re: Tonnage to KW
3.5 KW=1 ton refrigeration=12K BTU
95X3.5=332.5KW
06-09-2010, 08:33 PM #3
Re: Tonnage to KW
Cheers Chemi by 12k btu am i right that you mean 12000
06-09-2010, 11:33 PM #4
Re: Tonnage to KW
James10, 12k is short for 12,000.
07-09-2010, 07:55 AM #5
Re: Tonnage to KW
Not BTU or KBTU but rather BTU/h or KBTU/h because it's a rate of energy (power).
07-09-2010, 09:02 AM #6
Re: Tonnage to KW
Yeah Sandro, Isn't 1 british thermal unit raising 1 pound of water by 1 degree F/ hr? Having to dig into soggy memory now.
07-09-2010, 09:09 AM #7
Re: Tonnage to KW
Yes as you said...per hour
07-09-2010, 09:46 AM #8
Re: Tonnage to KW
God I love this site.......Btu's... I never knew thats what it implied. I knew it was British Thermal Unit....but not the "one pound of water raised by 1 degree F over 1 hour" its almost orgasmic the learning still going on...well ok I am getting a bit carried away.
08-09-2010, 04:39 AM #9
Re: Tonnage to KW
Kindergarten time, cheeez!
09-09-2010, 05:23 PM #10
Re: Tonnage to KW
tu Maybe for someone who know's the answer, We only know what we've been taught/self taught when we reach a problem surley it's better to find a solution than sit on it and not know the answer, I'm sure the first time you had to convert something ie pressures/temperatures you got this formula from somewhere or maybe you were born knowing I know i wasn't.
10-09-2010, 06:40 AM #11
13-09-2010, 09:27 PM #12
Re: Tonnage to KW
one ton of air conditioning = 12000 btu/hour
3,412 btu/hour = 1 kW
therefore kW = 12000/3413 tons
= 3.517 tons
or kW = tons x btuh/ton x kW/btuh
note that the units cancel, leaving kW
95 tons x 3.517 = 334 kW as noted by Chemi-Cool back in JuneLast edited by dougheret0; 13-09-2010 at 09:32 PM. Reason: small error
14-09-2010, 03:19 AM #13
Re: Tonnage to KW
Hi James.
No what ever intended, I trained back in the 60's with transition from imperial to SI metric. I bought a book as a reference guide. This is when slide rules were common, before calculators let alone computers.
Everything now is available on the net.
Calculating Tonnage of refrigeration machine
By batmon18 in forum CommercialReplies: 6Last Post: 09-06-2009, 11:21 PM -
steps on tonnage calc for split system
By Jimmy.Thurman in forum FundamentalsReplies: 1Last Post: 05-05-2009, 11:27 PM -
Tonnage for York Centrifugal YCCFCF27-CMF
By Hobagooday in forum Technical SpeculationsReplies: 0Last Post: 21-01-2009, 08:46 PM -
Large tonnage De-coupling
By MANIS in forum Technical DiscussionsReplies: 14Last Post: 14-08-2004, 06:29 PM -
Horsepower = Tonnage
By acman in forum FundamentalsReplies: 9Last Post: 31-05-2003, 03:10 PM