Thread: setting up txv
-
05-09-2010, 09:15 PM #1
setting up txv
i have a split system heat pump (american) 3 ton r410a. ive installed a txv in place of the piston type metering device. can someone give me some advice on the best way to go about proper adjustment of set screw. should i start with set screw turned all way in clockwise? can someone give me step by step instructions for this. any help will be greatly appreciated.
-
05-09-2010, 09:28 PM #2
Re: setting up txv
Hi Frankman,
Are you refering to the set screw on the txv itself?
If so there is generally no need to adjust it, it is there for the factory to adjust the valve before shipment. On very rare occasions it may need a tiny adjustment. I have never had to adjust one on a new valve with the correct orifice installed.
Ensure the bulb is installed correctly on clean pipe and insulated well and that the equalising line if fitted is also piped correctly.
-
05-09-2010, 09:44 PM #3
Re: setting up txv
the orifice comes out if adding external txv right?
-
05-09-2010, 10:27 PM #4
Re: setting up txv
Yes the fixed orifice or piston as i think its know in the States is replaced by the txv.
(The orifice i was refering to in my first reply is the one that goes in some makes of txv such as danfoss to size them for various system, they might also be called a cartridge or cage).
Is this a cooling only or heat pump system? Because things get complicated in a heat pump with the need for check valves etc if my understanding is correct, we don't get those design of systems here in the UK, its mostly mini splits which designed differently.
Jon
Similar Threads
-
setting up hot gas bypass valve for first time
By nick1986 in forum Air ConditioningReplies: 7Last Post: 14-04-2010, 09:28 AM -
TEV superheat setting and low temperatures
By DaBit in forum FundamentalsReplies: 11Last Post: 01-03-2010, 02:11 AM -
Setting Daikin VRV indoor unit fan speed
By mchild in forum Air ConditioningReplies: 8Last Post: 24-10-2009, 07:34 AM -
Manual Vi setting for Howden WRVi255
By desaipt2003 in forum Industrial CompressorsReplies: 13Last Post: 04-08-2009, 11:47 AM -
LP switch pressure setting for Pump Down of Chiller
By venugopal in forum Technical DiscussionsReplies: 9Last Post: 12-11-2006, 07:18 PM