    setting up txv



    i have a split system heat pump (american) 3 ton r410a. ive installed a txv in place of the piston type metering device. can someone give me some advice on the best way to go about proper adjustment of set screw. should i start with set screw turned all way in clockwise? can someone give me step by step instructions for this. any help will be greatly appreciated.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: setting up txv

    Hi Frankman,

    Are you refering to the set screw on the txv itself?
    If so there is generally no need to adjust it, it is there for the factory to adjust the valve before shipment. On very rare occasions it may need a tiny adjustment. I have never had to adjust one on a new valve with the correct orifice installed.

    Ensure the bulb is installed correctly on clean pipe and insulated well and that the equalising line if fitted is also piped correctly.

  3. #3
    Join Date
    Aug 2010
    Location
    usa
    Posts
    14
    Rep Power
    0

    Re: setting up txv

    the orifice comes out if adding external txv right?

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: setting up txv

    Yes the fixed orifice or piston as i think its know in the States is replaced by the txv.
    (The orifice i was refering to in my first reply is the one that goes in some makes of txv such as danfoss to size them for various system, they might also be called a cartridge or cage).

    Is this a cooling only or heat pump system? Because things get complicated in a heat pump with the need for check valves etc if my understanding is correct, we don't get those design of systems here in the UK, its mostly mini splits which designed differently.

    Jon

Similar Threads

  1. setting up hot gas bypass valve for first time
    By nick1986 in forum Air Conditioning
    Replies: 7
    Last Post: 14-04-2010, 09:28 AM
  2. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 02:11 AM
  3. Setting Daikin VRV indoor unit fan speed
    By mchild in forum Air Conditioning
    Replies: 8
    Last Post: 24-10-2009, 07:34 AM
  4. Manual Vi setting for Howden WRVi255
    By desaipt2003 in forum Industrial Compressors
    Replies: 13
    Last Post: 04-08-2009, 11:47 AM
  5. LP switch pressure setting for Pump Down of Chiller
    By venugopal in forum Technical Discussions
    Replies: 9
    Last Post: 12-11-2006, 07:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •