Results 1 to 12 of 12
    May 2004
    London, UK
    Lightbulb Cooling condenser of split with condensate from evaporator
    Would pumping condensate over the fins of the condenser in a split air conditioner result in a worthwhile improvement in efficiency?
    I'd have thought it would lower the pressure in the condenser and in turn help the compressor to pump more refrigerant vapour and lower the vacuum in the evaporator too.
    Also is the condensate likely to corrode the evaporator? I'd have thought not as it's basically distilled water, if the split is a heat pump the condenser in the outdoor unit will be designed to cope with condensate too.
    cheers,
    Pete.
    Apr 2001
    2,099
    27
    Re: Cooling condenser of split with condensate from evaporator
    I would say not worthwhile increase in efficiency, but it wont hurt matters.........
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
    Sep 2003
    ISRAEL
    72
    4,248
    The condensate water will rut the steel on the out door unit.
    Do not do it. You will gain nothing.
    Chemi
    Oct 2001
    Nottingham UK
    5,668
    yes it would as the condenser would lose heat adiabatically to evaporate the water.
    I'd have thought it would lower the pressure in the condenser[
    yes it would.
    On systems that operate with the suction in a vacuum, adiabatic cooling is not normally required
    I thought we were talking about running condensate over the condenser coil?
    Split systems don't normally run with the suction in a vacuum
    The problem with using water to cool the condenser is mostly related to Legionella. The water not evaporated tends to collect in a pool below the condenser coil and in certain circumstances Legionella spores can be circulated by the condenser fan.
    Is it worth the hassel?
    May 2004
    London, UK
    Quote Originally Posted by frank
    Oops, quite correct I meant condenser.
    I see, so the evaporator is at a lower pressure than the condenser, rather than being in a vacuum?
    So lowering pressure in the condenser would allow the compressor to pump more refrigerant vapour, in turn lowering pressure in the evaporator.
    Still the cooling depends on the amount of liquid refrigerant going through the capilliary/expansion valve, so would the above increase this?
    True, although problems only occur when the bacteria is 'aerosolised' such as in a cooling tower, shower head or even peat dust(!). Evaporative coolers could cause problems with legionella but have a history of safety as the water is not turned into a spray.
    Might be worth trying out with some distilled water on the condenser to see if it lowers the air temperature from the evaporator.
    cheers,
    Pete.
    Aug 2004
    Holland
    55
    Some Airconditioners are actually designed for this.
    They can be recognized bij a connection on the side of the bottom tray of the condesing unit end the fan is fitted with a ring on the edges op the fanblades.
    This ring picks up the water en spray it on to the condensor.
    It has a big effect on the capacity.
    With extreem hot weather like past days it is a difference of a blazing hot liquid line or a reasonable cold liquid line.
    The condensor should not be soaked with water but just lightly moist.
    If you want to try it out, take a whatever condensor of a small unit, connect your gauges, take a spraying flask, take the pressure readings, spray some water on the condensor and see how the pressure lowers.
    Victor
    Oct 2001
    Nottingham UK
    5,668
    I think you will find that all evaporative condensers enhance their cooling capacity by the fact that water "spray" is drawn onto the coil by the fans. Adiabatic coolers have water trickled down a series of "filters" where the air passing through the "filters" is cooled adiabatically.
    The water that is "misted" onto an evaporative condenser usually passes through some sort of water treatment process to kill the bacteria (mostly UV light) but it is the water that collects under the coil, either in the drain pan or on the floor that "ponds" and that can be the cause of Legionella. This needs to be treated as well.
    Oct 2001
    Nottingham UK
    5,668
    The amount of liquid refrigerant passing through the metering device is not increased by the condenser being cooled more. The refrigerant quality is enhanced. With a lower liquid temperature during high ambients you get an increase in refrigeration duty. This can be seen on a Mollier chart.
    rbartlett's Avatar
    rbartlett Guest
    All window rattlers are designed with slinger rings on the condenser fan and condensers are sized accordingly
    Unless in a particulary hot climate the addition of water to a clean condenser on a modern 'japanese' type split is totally unncessary -most in the UK are over condensing enough already- as they are all designed to 46 deg'c operation.
    The addition of water on an already over efficient condenser will lower the refrigerant pressure/flow, reducing capacity and increase the chance of icing on the evaparator.
    This is why most splits need F.S.C for comms rooms etc during winter
    Don't do it...don't bother........
    Richard
    May 2004
    London, UK
    Thanks for the replies.
    So it looks like cooling the condenser would increase the enthalpy of the refrigerant, but will also reduce the capacity of the system in a conventional split as the pressure forcing refrigerant through the capilliary will be lower.
    I expect the newer 'inverter' splits with a linear expansion valve might benefit though.
    Also trickling the water over the coil for adiabatic cooling instead of spraying it would give less potential for problems with Legionella.
    cheers,
    Pete.
    Apr 2005
    INDIA
    63
    84
    Quote Originally Posted by smileypete
    cheers,
    Pete.
    MR, SIMLY,
    WORTH EXPERIMENTING , not to use , if not designed for moist spray, time pass.
    beni joseph,
    Mar 2002
    Sydney Australia :D
    47
    Lightbulb Re: Cooling condenser of split with condensate from evaporator
    cheers,
    Pete.
    If the ambient temp is high enough for the system to require the condense to be discharged onto the condenser unit then it will surely evaporate before any bacteria can cause a problem.
    Also heat pumps produce water in heating mode so provision is made for water to drain away, thus removing the chance of water build up & growth of bacteria.
    If the ambient temp is below 30c then there is no need for the condense to be directed onto the condenser, but could in theory aid in high temps providing that the flow was of a suitable level. More than likely it will not be great enough to have any noticeable effect.
    :cool: Do the job once & do it right. :cool:
  1. Condensor split temperature
    By Peter_1 in forum Fundamentals
    Last Post: 31-07-2011, 05:49 PM
  2. Evaporative Condenser in reverse cycle
    By Friobernal in forum Industrial
    Last Post: 16-04-2009, 02:06 PM
  3. How to controll Logarithmic Mean Temperature of evaporator
    By Josip in forum Technical Speculations
    Last Post: 19-08-2006, 12:15 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Last Post: 13-10-2005, 05:14 AM