05-09-2010, 03:22 PM #1
split system charging
after installing a split system more refrigerant is needed based on the length of the line set. the amount of extra ***** needed to add is based on liquid line size right? does it matter what the suction line size is? for instance the manufacturer states that the condensing unit is charged with 180 oz of refrigerant for up to 15 feet of line set, but if you have a 45 foot line set you have to add ***** for 30 more feet of line set. the liquid line size is 3/8 size and the suction lin size is 3/4 on the system im referring to.
-
05-09-2010, 03:50 PM #2
Re: split system charging
Are you using the same size tubing that the unit is designed for?
Is the total length (between the indoor and outdoor, not liquid line length added to suction line length) under the permissable total length stated by the manufacturer?
If same pipe diameter, if not over the maximum range, the extra charge required as stated by the manufacturer is for the extra difference in distance between the indoor and outdoor units. They already assume suction and liquid lines to be the same length and have factored that into their extra charge required.
So if you are using the same size piping, then you add ***** for 30 more feet.Last edited by paul_h; 05-09-2010 at 03:53 PM.
-
05-09-2010, 03:56 PM #3
Re: split system charging
Is this a mini split or an American style system to a central ducted air handler?
Mini split like we get over here and its grams per meter over the pre charged lenght, central air and it can be off a chart, or done with subcooling or superheat depending on the expansion device.
-
05-09-2010, 04:27 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: split system charging
..........................
Last edited by nike123; 05-09-2010 at 04:30 PM.
-
05-09-2010, 04:30 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
05-09-2010, 05:27 PM #6
Re: split system charging
i know you add ***** for 30 more feet but how do you know how many ounces to add for the 30 feet.
-
05-09-2010, 05:31 PM #7
Re: split system charging
this is american style split system heat pump r22 3 ton.
-
05-09-2010, 06:17 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
15-11-2010, 03:24 PM #9
Re: split system charging
Correct, the install manual will tell you how many grams per Meter or foot. There are tons of video's out there to help you.
Last edited by frank; 15-11-2010 at 05:23 PM.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Lost Remote Control for Split System AC
By kiamaian in forum Air ConditioningReplies: 5Last Post: 12-04-2009, 06:12 PM -
Heating not working on split system what is the problem?
By airflo in forum Air ConditioningReplies: 10Last Post: 22-07-2008, 06:42 PM -
Charging system with TEV
By ahl in forum CommercialReplies: 6Last Post: 14-07-2008, 03:53 PM -
System charging
By Dylan in forum FundamentalsReplies: 10Last Post: 17-12-2004, 10:37 PM