    split system charging



    after installing a split system more refrigerant is needed based on the length of the line set. the amount of extra ***** needed to add is based on liquid line size right? does it matter what the suction line size is? for instance the manufacturer states that the condensing unit is charged with 180 oz of refrigerant for up to 15 feet of line set, but if you have a 45 foot line set you have to add ***** for 30 more feet of line set. the liquid line size is 3/8 size and the suction lin size is 3/4 on the system im referring to.



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: split system charging

    Are you using the same size tubing that the unit is designed for?
    Is the total length (between the indoor and outdoor, not liquid line length added to suction line length) under the permissable total length stated by the manufacturer?

    If same pipe diameter, if not over the maximum range, the extra charge required as stated by the manufacturer is for the extra difference in distance between the indoor and outdoor units. They already assume suction and liquid lines to be the same length and have factored that into their extra charge required.

    So if you are using the same size piping, then you add ***** for 30 more feet.
    Last edited by paul_h; 05-09-2010 at 03:53 PM.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: split system charging

    Is this a mini split or an American style system to a central ducted air handler?

    Mini split like we get over here and its grams per meter over the pre charged lenght, central air and it can be off a chart, or done with subcooling or superheat depending on the expansion device.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: split system charging

    ..........................
    Last edited by nike123; 05-09-2010 at 04:30 PM.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: split system charging

    Quote Originally Posted by frankman View Post
    after installing a split system more refrigerant is needed based on the length of the line set. the amount of extra ***** needed to add is based on liquid line size right? does it matter what the suction line size is?
    No, it does not much.
    Volume of evaporated refrigerant is many times higher than volume of liquid refrigerant.
    For example 1 kg liquid R410 at 4°C bulb point is 0,86 l volume and 10K superheated vapor is 32,3 l.

  6. #6
    Join Date
    Aug 2010
    Location
    usa
    Posts
    14
    Rep Power
    0

    Re: split system charging

    i know you add ***** for 30 more feet but how do you know how many ounces to add for the 30 feet.

  7. #7
    Join Date
    Aug 2010
    Location
    usa
    Posts
    14
    Rep Power
    0

    Re: split system charging

    this is american style split system heat pump r22 3 ton.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: split system charging

    Quote Originally Posted by frankman View Post
    this is american style split system heat pump r22 3 ton.
    Then you charge by superheat table or weight stated in instalation manual.

  9. #9
    Join Date
    Sep 2010
    Location
    USA
    Age
    43
    Posts
    13
    Rep Power
    0

    Re: split system charging

    Correct, the install manual will tell you how many grams per Meter or foot. There are tons of video's out there to help you.
    Last edited by frank; 15-11-2010 at 05:23 PM.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Lost Remote Control for Split System AC
    By kiamaian in forum Air Conditioning
    Replies: 5
    Last Post: 12-04-2009, 06:12 PM
  3. Heating not working on split system what is the problem?
    By airflo in forum Air Conditioning
    Replies: 10
    Last Post: 22-07-2008, 06:42 PM
  4. Charging system with TEV
    By ahl in forum Commercial
    Replies: 6
    Last Post: 14-07-2008, 03:53 PM
  5. System charging
    By Dylan in forum Fundamentals
    Replies: 10
    Last Post: 17-12-2004, 10:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •