    Sizing Calc but not as we know it



    Hi guys
    I'm new to the site and am looking for a bit of info on sizing a unit for a security lodge. I've used the dean and wood calc prog , but I have some minor doubts over the accuracy . Any help gratefully appreciated, as you will have noticed I did say security lodge , by that I mean approx 45% glass 50% brick 5% who knows. it has a ceiling of 2.9m but above that not an attic but a similar kind of void , the problem I feel here is that there is a tin cladded apex style roof. As you will appreciate dean and woods calc program is ok until you get the odd buildings like this.
    Floor area is 5m x 1.9m . I can't use a rule of thumb due to the damn place being like a conservatory. I have tried to read as many threads as possible over the last hour but my eyes are glazing.
    Thanks guys



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Sizing Calc but not as we know it

    size it for a high load 200 watts per m2

    you will be close enough if not a tad over

    cheers

    richard

  3. #3
    Join Date
    Jun 2005
    Location
    Lancs
    Age
    61
    Posts
    21
    Rep Power
    0

    Smile Re: Sizing Calc but not as we know it

    Much appreciated
    Cheers
    Steve

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Sizing Calc but not as we know it

    CIBSE rule of thumb is 125w/m2 which is on the high side so 200w/m2 as Richard suggests will definately cover a security building.

    (Gymnasiums = 300w/m2)
    (Server Rooms = 400w/m2)

Similar Threads

  1. Piping and line sizing in lbs/min
    By Kathleen in forum Tools and Calculators
    Replies: 18
    Last Post: 29-05-2009, 03:07 PM
  2. Compressor sizing using R404a
    By PCL in forum Refrigerants
    Replies: 4
    Last Post: 14-08-2006, 11:09 PM
  3. Sizing for Australia
    By dogma in forum Fundamentals
    Replies: 5
    Last Post: 17-03-2006, 11:05 AM
  4. 134a surge drum sizing
    By Camille in forum Refrigerants
    Replies: 0
    Last Post: 03-03-2006, 02:44 PM
  5. sizing of low temp refrigeration cabinets
    By DALO in forum Technical Speculations
    Replies: 4
    Last Post: 15-01-2006, 09:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •