Results 1 to 4 of 4
-
04-09-2010, 07:46 AM #1
refrigeration reach in split system w/ multiple evaps
Hello, Im an air condtioning mech. need a little input on a reach in R22 split system with six omnitemp fan powerd evaporators controlled with a liquidline solinod valve opening and closing with a remote bulb tstat highside press 290psi, lowside press.65psi.... the sight glass is flashing. cannot get reachin box temp below 45.. (trying to achieve 41degrees or lower)
-
04-09-2010, 09:20 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: refrigeration reach in split system w/ multiple evaps
Where is filter drier placed? After or before sight glass? First ensure that condenser is clean and you have proper air flow and all solenoids are open.
Then check your subcooling and if not 5-6K charge gas until subcooling at condenser outlet is about 5-6K. Than check your sight glass. If it is placed after filter-drier and still flashing, than check temperature difference between filter inlet and outlet. It must be lower than 2K. If it is higher than 2K, change filter-drier.Last edited by nike123; 04-09-2010 at 09:32 AM.
-
10-09-2010, 04:14 AM #3
Re: refrigeration reach in split system w/ multiple evaps
We need to know the temps of the air entering and leaving the evaps and cond, as well as the liquid line temp and the suction line temp at the TXV bulb.
-
10-09-2010, 02:12 PM #4
Re: refrigeration reach in split system w/ multiple evaps
I'll also add this.
Is this a new system or has it worked in the past?
What is the model of the condensing unit and the OmniTemp evaps (probably OTM's)Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
SOS!!!! HOW TO calculate refrigeration system and choose refrigeration Accessori
By ashp in forum Refrigeration BooksReplies: 9Last Post: 30-11-2009, 10:08 AM -
Refrigeration system charge calculation query.
By refriengr in forum FundamentalsReplies: 0Last Post: 29-05-2008, 08:03 PM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM