    Co2 rack



    Started a co2 rack a few weeks ago. Sub critical 134A top cycle RDM controller. Here is the problem. The company that is programming the RDM is having a hard time fine tuning the sporlan steppers on the cascade evaps. Granted this is a learning process. The medium temp is liquid and low temp dx. The problem is top cycle starts to loose control and the electronic valves open too fast flood condenser floodback occurs starts to pinch down the valves superheat goes up co2 cannot condense vessel pressure rises etc I notice things happen very quick with co2 ex; loading cases systems coming out of defrost etc. I know the valves are oversized on the evap condensers. The guys doing the programming have been working on this for weeks. It's still not right and grand opening is soon. I'm getting bummed out



  2. #2
    Join Date
    Aug 2008
    Location
    California
    Posts
    28
    Rep Power
    0

    Re: Co2 rack

    The Sporlan Steper motors are usually controlled by a PID loop(proportional, integral, and derivative) . Setting up a PID loop is more an art than a science and needs to be turned for every application.
    I suggest you read up on PID controls.

    Remember that refrigeration is a slow process (in computer terms), therefore use small numbers.

    Also for starters set I = 0, and focus on getting a stable system (not necessarily the correct temp but just a stable system).

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Co2 rack

    Welcome in the wonderful world of carbon dioxide refrigeration.

  4. #4
    Join Date
    Jan 2007
    Location
    USA
    Age
    58
    Posts
    145
    Rep Power
    18

    Re: Co2 rack

    Decosta, I understand pid. The dance between the top and bottom cycle is a tricky one and is dependent upon the superheat remaining low and tight on your heat exchngers. First time seeing CO2 in a refer system. We have it working well now.

Similar Threads

  1. Rack cannot reach low or medium setpoints
    By Hotdoggy in forum Trouble Shooting
    Replies: 2
    Last Post: 28-06-2010, 10:51 PM
  2. Supermarket rack oil reservoir question
    By friocold2008 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 05-12-2009, 08:38 AM
  3. "Unstable" Rack Receiver Liquid Level
    By chweber in forum Commercial
    Replies: 3
    Last Post: 09-02-2009, 09:58 AM
  4. Refrigerant quality in rack systems?
    By round_the_rack in forum Supermarket Refrigeration
    Replies: 6
    Last Post: 16-07-2008, 05:20 PM
  5. R744 Supermarket Rack
    By 750 Valve in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 28-07-2006, 03:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •