Thread: Co2 rack
    Jan 2007
    52
    145
    11
    Co2 rack
    Started a co2 rack a few weeks ago. Sub critical 134A top cycle RDM controller. Here is the problem. The company that is programming the RDM is having a hard time fine tuning the sporlan steppers on the cascade evaps. Granted this is a learning process. The medium temp is liquid and low temp dx. The problem is top cycle starts to loose control and the electronic valves open too fast flood condenser floodback occurs starts to pinch down the valves superheat goes up co2 cannot condense vessel pressure rises etc I notice things happen very quick with co2 ex; loading cases systems coming out of defrost etc. I know the valves are oversized on the evap condensers. The guys doing the programming have been working on this for weeks. It's still not right and grand opening is soon. I'm getting bummed out
    Aug 2008
    California
    28
    Re: Co2 rack
    The Sporlan Steper motors are usually controlled by a PID loop(proportional, integral, and derivative) . Setting up a PID loop is more an art than a science and needs to be turned for every application.
    I suggest you read up on PID controls.
    Remember that refrigeration is a slow process (in computer terms), therefore use small numbers.
    Also for starters set I = 0, and focus on getting a stable system (not necessarily the correct temp but just a stable system).
    Mar 2006
    Merate (LC) - Italy
    2,553
    Re: Co2 rack
    Welcome in the wonderful world of carbon dioxide refrigeration.
    Jan 2007
    52
    145
    11
    Re: Co2 rack
    Decosta, I understand pid. The dance between the top and bottom cycle is a tricky one and is dependent upon the superheat remaining low and tight on your heat exchngers. First time seeing CO2 in a refer system. We have it working well now.
  1. Rack cannot reach low or medium setpoints
    By Hotdoggy in forum Trouble Shooting
    Last Post: 28-06-2010, 10:51 PM
  2. Supermarket rack oil reservoir question
    By friocold2008 in forum Supermarket Refrigeration
    Last Post: 05-12-2009, 07:38 AM
  3. "Unstable" Rack Receiver Liquid Level
    By chweber in forum Commercial
    Last Post: 09-02-2009, 08:58 AM
  4. Refrigerant quality in rack systems?
    By round_the_rack in forum Supermarket Refrigeration
    Last Post: 16-07-2008, 05:20 PM
  5. R744 Supermarket Rack
    By 750 Valve in forum Supermarket Refrigeration
    Last Post: 28-07-2006, 03:32 AM