i would never do this of course but i have heard stories of flushing the line set on new install with r410a instead of using a vacuum pump to evacuate moister from the lines. than charge the 410a and done.
is this a bad idea? dose it actually get rid of the moister?
-
02-09-2010, 03:56 PM #2
-
10-10-2010, 09:24 AM #3
-
02-09-2010, 03:56 PM #4
Re: charging R410a with no vacuum !!
Apart from being a felony in environmentally concerned countries (other than US), it is useless (R410A doesn't have any appreciable hygroscopic capacity) and expensive (R410A is more much more costly than OFN).
toprunner: you can't do that in Sweden.
-
02-09-2010, 04:00 PM #5
-
02-09-2010, 04:06 PM #6
Re: charging R410a with no vacuum !!
Under EU regulations, you can't use refrigerant to flush pipes and to deliberately release it into the atmosphere. Full stop.
Your opinion is pure and unlawful speculation.
-
02-09-2010, 04:15 PM #7
-
10-10-2010, 12:33 AM #8
-
02-09-2010, 04:24 PM #9
Re: charging R410a with no vacuum !!
I meant fluorinated refrigerants, of course.
-
02-09-2010, 04:27 PM #10
-
10-10-2010, 12:34 AM #11
-
02-09-2010, 04:56 PM #12
Re: charging R410a with no vacuum !!
well doperunner < sorry top< how glad I am to be out of the trade , < with idiot ideas like you have, what was the saying? I am all right jack
-
03-09-2010, 08:05 AM #13
-
03-09-2010, 08:37 AM #14
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: charging R410a with no vacuum !!
@ toprunner
With what magical membrane in front of flushing agent (whatever it is) you think you are pushing moisture and air from system by flushing it?
Do you think that you discovered America with your "advanced cheap method" and all other "stupid engineers who vacuuming properly their systems" are some idiots who follow some new religion?
Or you just another hack around corner who think that whole RAC industry are just morons.Last edited by nike123; 03-09-2010 at 08:47 AM.
-
03-09-2010, 09:13 AM #15
Re: charging R410a with no vacuum !!
Just talking from experience. I use vacuum when its necessary and i dont see a reason when mounting a pre-charged R410a unit. Many do same as me and at least i never had a problem. I see more problem from the schraeder you need to put to be able to evacuate with vacuumpump.
I never say you can remove moisture .. just that if you make a clever installation procedure its not necessary and you can flush instead. I think thats what the original post was about.
Try to clean your language.. your arguments falls.
-
03-09-2010, 09:35 AM #16
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: charging R410a with no vacuum !!
My language is clean, I don't see any dirty word.
My arguments are good. Try this way:
Acceptable moisture level is 10 ppm. That is achieved when end vacuum is below 1000 microns.
What is your moisture level after flushing? You don't know, don't you? I know by monitoring my vacuum level.
Do you need more arguments?Last edited by nike123; 03-09-2010 at 09:45 AM.
-
03-09-2010, 09:53 AM #17
Re: charging R410a with no vacuum !!
This is an awesome thread!
Toprunner, how can you break the law and go against every inch of good practice and still fight your point?
Amazing!
-
02-09-2010, 05:16 PM #18
Re: charging R410a with no vacuum !!
I'm not a mod, but let's try to keep this a civil exchange of opinions.
EDIT: unable to keep it civilLast edited by NoNickName; 02-09-2010 at 09:56 PM.
-
04-10-2010, 03:57 PM #19
Re: charging R410a with no vacuum !!
Flushing with ofn or any other gas can't get rid of moisture. You pull a deep vacuum so that the moisture boils off in the system and the pump can pull it out. If u got a call for a system that u knew had moisture in it would u just dump bottle after bottle into the sytem trying to flush it or would u pull a vacuum???
-
30-10-2010, 05:50 AM #20
Re: charging R410a with no vacuum !!
Flushing with ofn or any other gas can't get rid of moisture. You pull a deep vacuum so that the moisture boils off in the system and the pump can pull it out. If u got a call for a system that u knew had moisture in it would u just dump bottle after bottle into the sytem trying to flush it or would u pull a vacuum???
-
02-09-2010, 08:50 PM #21
Re: charging R410a with no vacuum !!
Flushing with ofn or any other gas can't get rid of moisture. You pull a deep vacuum so that the moisture boils off in the system and the pump can pull it out. If u got a call for a system that u knew had moisture in it would u just dump bottle after bottle into the sytem trying to flush it or would u pull a vacuum???
-
10-10-2010, 09:46 AM #22
Re: charging R410a with no vacuum !!
Hello ktm,
flushing with OFN and a vacumn pump will remove moisture. Please see my proceedure below.
1/Strength test the system.
2/Reduce to leak test pressure and leak test with soapy water (dependant on local legislation you could have added a trace gas and used an electronic detector at this point).
3/Blow off the OFN at a safe point, to flush the system of moisture droplets and debri.
4/fit vacumn pump with screider valve core removed (or on a service port or dedicated service valve). Make sure you have no leaks in the gauge line, vac them on the pump and do a drop test on them before you start.
5/vacumn down to 2500 microns with the gas balast valve open on the pump (slow vacumn).
6/break vacumn with OFN to 0psig
7/repeat 5
8/Carry out a drop test (pump off, watch vacumn level for slow or quick rise).
9/If the rise is quick check for leaks, moderate repeat 6, if slow close balast and vacumn to below 1000 microns.
10/Drop test again, if rise is moderate repeat 6, if slow vacumn to final required micon level 50 to 500 microns dependant on syatem size and refrigerant (500 may even be lower than required for ammonia).
Don't forget the vacumn should have clean oil and be gererally in a good servicible order.
If you want quick vacumn add heat by heating the indoor unit (or running evaporator fans if you can).
There is a right way and a wrong way to do most things and areas in between, but if you want the manufacturer to honour the warranty on their equipment you need to try and keep the pipework clean on instal (purge with OFN and keep the pipe ends sealed when you are not working on it) and pressure test and evacuate your equipment
Kind Regards Andy DIf you can't fix it leave it that no one else will:rolleyes:
-
02-09-2010, 09:54 PM #23
Re: charging R410a with no vacuum !!
Ok, guys, you are really pissing me off. You must think that here we are all stupid or something. At first, the genius that fills 200g of F-gas and then pulls the vacuum, then here it comes the irish that thinks doing a blowjob of nitrogen to remove the moisture is not right.
Do you f---ing read what I wrote? Fill it up with nitrogen, warm it up and then pull the vacuum.
And if I got the call for moisture in the system, NO I DON'T PULL THE VACUUM. I try first to understand where the moisture is coming from, fix the system that some f---ing irish or swedish engineer was not able to, pressurise the system, and if ok only then pull the vacuum.
-
03-09-2010, 08:03 AM #24
Re: charging R410a with no vacuum !!
Have you read the original post ? Its about flushing lines in a new installallation.
Anyone can buy and install a split unit here in Sweden. If you think they buy a vacuumpump at the same time you are either naive... or **** . What laws are they breaking if they have no certificate ?
-
02-09-2010, 10:40 PM #25
Re: charging R410a with no vacuum !!
Don't take it personally NNN, there seem to be a lot of Trolls around at the moment.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
03-09-2010, 08:23 AM #26
Re: charging R410a with no vacuum !!
Sorry for my comment NNN it obviously hit a nerve. Of course I wouldn't expect someone to evacuate a system with moisture in it without finding out how it got in the system. My point was that alot of peole don't work to the same standards as perhaps you or I. Even when it is against the law as you well point out. Once again sorry I pissed u off so much but I never taught my post would upset u so much.
-
03-09-2010, 09:22 AM #27
Re: charging R410a with no vacuum !!
I think toprunner and reptile make a good pair,maybe they should open a business together.oh,,,,at least reptile has a vac pump and uses it.
-
03-09-2010, 09:38 AM #28
-
03-09-2010, 10:19 AM #29
Re: charging R410a with no vacuum !!
Hey guys, can you hold it for 10mins? that's the time it takes me to go out and buy more popcorns... I ate them all already!!
-
03-09-2010, 05:05 PM #30
Re: charging R410a with no vacuum !!
The whole idea with vacuum procedure is to make water boil at lower temperature and suck out the vapour......
Sublimation and evaporation is not caused by vacuum..its from diffusion and sunradiation.
-
03-09-2010, 05:27 PM #31
Re: charging R410a with no vacuum !!
Why not read the Kyoto Protocol on the weekend and learn more?
NNN is absolutely right!
And one little thigy, any moisture remain in the system will shorten the life expectancy of the compressor as the POE oil is very hygroscopic.
-
04-09-2010, 12:24 AM #32
-
04-09-2010, 12:36 PM #33
Re: charging R410a with no vacuum !!
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
04-09-2010, 09:41 PM #34
Re: charging R410a with no vacuum !!
I will never forget Copenhagen. It was one of the biggest jokes i ever seen.
I not say Global Warming is a fraud. I said AGW is.. if you read that bad .. what you doing in a parlament?
The hypothese that man can change global temperature is proven wrong. The temperatur change as it always does. We still see a continous warming since last ice-age.
-
04-09-2010, 12:19 AM #35
-
04-09-2010, 03:21 AM #36
Re: charging R410a with no vacuum !!
People were evacuating lines with a vac pump before any enviromental policy was made law, because it's needed to remove moisture to prevent damage to the system.
Also unfortunately pre charged splits don't even have driers, so more important to vac them out than any other type of a/c
Over 10 years ago when splits were only installed by proper refrig tradespeople, they seem to last 12 years or more.
These days where almost anyone installs splits, lucky if they last 5 yrs, coincedence?
-
04-09-2010, 11:35 AM #37
Re: charging R410a with no vacuum !!
Of course you put a filter in if you choose to flush it. Its a safer procedure than evacuate in cold weather.
I can add that we teach all technicians here in sweden how to remove moisture below 15 degree in reasonable time, its a part of education. Your procedure is not sufficient.
-
04-09-2010, 12:27 PM #38
Re: charging R410a with no vacuum !!
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
04-09-2010, 09:36 PM #39
Re: charging R410a with no vacuum !!
I told problem start at 15 degree and get worse with lower temperature. Where did you get 30 degree from?
Check a diagram for boilingpoint of water and a IX-diagram for condensation if you dont understand what i talk about. (you obviously dont)
Yes.. i teach technicians sometimes.
-
05-09-2010, 11:50 AM #40
-
04-09-2010, 10:14 AM #41
Re: charging R410a with no vacuum !!
Let's remain to what it is. Evacuating refrigerant F-gas is forbidden. Full stop. Please comply.
-
04-09-2010, 11:36 AM #42
-
04-09-2010, 08:51 PM #43
Re: charging R410a with no vacuum !!
Leakages, losses of ***** have been happening and will be, unfortunately, but, one who deliberately is letting himself let into the air up to 200 gr of it by every A/C he installs (and in a year he may install tens of A/C's or worse, if he leads a business, by the hands of his people - hundreds of A/C's) and by that remain happy and proud of himself with such doings, is utterly wrong.
It seems Toprunner confuses moisture in a system (grams in a big, usually less of a gr) with the water comets consist of. The latter, indeed, travel the space for thousands of years seemingly untouched by
cosmic vacuum, but the scale is different - the comets' masses are millions of tons - compared to our gram in the system which are subjected to the very comparable degree of the "artificial" vacuum.
-
04-09-2010, 09:46 PM #44
-
05-09-2010, 07:59 AM #45
Re: charging R410a with no vacuum !!
Answer once your own question above...what happens to moisture when it's cold? I bet you will give the wrong answer, seeing the reply you have to Yuri B.
In one of your post, you said you have to evacuate below 15°C and you teach that to technicians, again, this is against EN regulations.
You can't evacuate to a temperature and if you meant the vapor pressure of water at 15°C, even then this is completely fault. What says Swedish and EN regulations about this? You know the law so good you said
Prove me also once the 200 gr rule of Sweden.
I seriously doubt your certificate, I think you bought it somewhere.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
05-09-2010, 11:36 AM #46
Re: charging R410a with no vacuum !!
Sorry,,, i dont understand what you write here but i dont recognice my words.. please cut and paste instead of try to phrase me.
There is no rule... we have recommendations and intstructions. We dont leaktest with F-gas by a rule... its one of many options and allowed.
You have a funny way of putting words in my mouth that i never said... is that your way of moderate this forum? Its very rude.
-
14-12-2010, 07:31 AM #47
Re: charging R410a with no vacuum !!
[quote=toprunner;201831]Sorry,,, i dont understand what you write here but i dont recognice my words.. please cut and paste instead of try to phrase me.
There is no rule... we have recommendations and intstructions. We dont leaktest with F-gas by a rule... its one of many options and allowed.quote]
Toprunner,
I think Peter has just asked you several times to show where did you read that you are allowed to use 200gr of f-gases to trace a leak. I copied and pasted you words, if you are allowed, ther should be a paper in which that practice is written. The question is quite simple, hence the answer should be as well.
IMHO, more than one guy here is expecting that answer, as it would be against all regulations we do know, and, Sweden, for sure, must not be different from our countries.
Regards,
Nando.
-
04-10-2010, 03:58 PM #48
Re: charging R410a with no vacuum !!
It is not possible to discuss Swedish regulation with you since you have no idea about it. There has been some kind of certificate to work with refrigerants since beginning of the 90´s in Sweden (after Montreal).. i dont know exact year but my first was from 1995. The first certificates were much harder and more restricted then the latest. Since the EU rules came its much more easy and the certificate is now personal. Before we needed both one each person and one ackreditationprocedure for the company that empolys technicians and handle gas containers.
-
05-09-2010, 03:19 AM #49
Re: charging R410a with no vacuum !!
I fully support NNN.
Add to that a good purge is not good enough.
-
06-09-2010, 09:59 AM #50
Re: charging R410a with no vacuum !!
This thread has gone berserk. Cancelling subscription.
Similar Threads
-
Vacuum Pump Questions
By position1 in forum FundamentalsReplies: 7Last Post: 08-10-2009, 02:33 AM -
Vac Down Procedure.
By mendoza in forum FundamentalsReplies: 3Last Post: 26-09-2009, 04:19 PM -
Troubleshooting a vacuum pump and gauge set.
By Old Codger in forum FundamentalsReplies: 7Last Post: 08-08-2008, 05:13 PM -
inverters pulling vacuum
By bangoman in forum Air ConditioningReplies: 2Last Post: 05-02-2008, 09:12 PM -
charging R410a
By cikku in forum RefrigerantsReplies: 25Last Post: 05-12-2005, 12:32 AM