    Receiver Design



    Hi, I am doing final year for chemical engineering and assigned to do a detail design of a receiver. This receiver thing is new to me and I have no idea how to start, then I came across this forum and hoping someone would help me or give me a suggestion how to start.

    I guess first thing is, I need to find out how big my receiver will be, but I'm not quite sure how to find it out since my refrigeration cycle was done in HYSYS simulation.

    Regards,

    Budi



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Receiver Design

    A liquid receiver is a simple vessel with two ports.
    The inlet receives the broth (oil, refrigerant, foam, ecc) from the condenser and simply pours it into the liquid pool.
    The outlet is getting liquid from the bottom of the vessel through a pick up pipe, to ensure liquid only is "fished".

    The criteria for designing a receivers are: the safety pressure to which it will be subject, the volume required and the type of connections for inlet and outlet.

  3. #3
    Join Date
    Sep 2010
    Location
    Australia
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: Receiver Design

    I see. Is it more like a vertical or a horizontal vessel? And how do I decide what type of connections and what are the choices available? Do you have any good sources for my references for this design?

    Thanks a lot for the reply.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Receiver Design

    Vertical are widely more spread, but horizontal is also possible. For the connections, either welded lap joints or rotalock connections are used. Try with some receiver manufactuer website. Here in Italy frigomec is very common, but Onda is also a known producer.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Receiver Design

    Quote Originally Posted by Budi View Post
    I see. Is it more like a vertical or a horizontal vessel? And how do I decide what type of connections and what are the choices available? Do you have any good sources for my references for this design?

    Thanks a lot for the reply.
    Ready made source here...

    http://tinyurl.com/3xw4qh4
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Sep 2010
    Location
    Australia
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: Receiver Design

    ok, thanks a lot. I will try to design it. I'll get back here if I'm stuck again. Thanks Brian, that was how I found this site, haha

  7. #7
    Join Date
    Sep 2010
    Location
    Australia
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: Receiver Design

    Hi again. I'm a bit confused about the pressure I'm designing for. In a book, I read that in the receiver, there should be around 50-80% liquid and the rest is in vapour phase..

    But at the outlet temperature and pressure of condenser (inlet of receiver), there shouldnt be any vapour forming. Do I specify the design pressure to be lower than it is? or do I design for a higher temperature? My output temperature from condenser is 33C and the plant is in tropical area. Therefore the temperature wont vary a lot thourghout the year.

    Thanks

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Receiver Design

    Hi Budi.
    in Australia and NZ, receiver vessels are classified as unfired pressure vessels and designed to BS5500 specification that includes design working temperature limits and design and testing pressure limitations. Any design has to be certified and approved before manufacture, then tested and issued with a design number and approval, then after manufacture tested and crowned, all material and welding procedures, and a mountain of paperwork envolved.

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Receiver Design

    The liquid receiver can be almost empty or almost full... it doesn't matter what amount of refrigerant is inside.
    Vapour is in equilibrium at the same pressure than liquid. It's called two-phase equilibrium.

  10. #10
    Join Date
    Sep 2010
    Location
    Australia
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: Receiver Design

    Hi guys, now that I have finished the mechanical design for this receiver, I move on to the Piping & Instrumentation Diagram section. I need some advice on how to control the receiver. If i want to control the pressure by using pressure relief valve, or control the level by using a drain, the total refrigerant in my refrigeration system will be less. If i add a buffer tank or something, then the receiver would not serve its purpose right?

    I'm trying not too change the refrigerant flow rate as it might affect the downstream process (duty required for other part of the plant)

    Thanks for the helps

    Regards,
    Budi

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Receiver Design

    No P&I or regulation required for a refrigerant receiver. You can't even regulate the pressure: it's a vessel.

  12. #12
    Join Date
    Aug 2010
    Location
    USA
    Age
    54
    Posts
    10
    Rep Power
    0

    Re: Receiver Design

    Budi, I don't know of any Refrigeration system that would control the receiver, there is nothing to control, it is just a storage receptacle for excess refrigerant in the system at a any time.

    The refrigerant liquid level changes with time according to the operating condition of the system (ambient temp, refrigeration load, system displacement).That is why you have the receiver because if you have level of liquid refrigerant you can assure a the liquid line is being fed full liquid refrigerant.

    The relief valve is just for safety in case the pressure within the receiver rises to a dangerous level. These valves vent to the atmosphere or to a secondary vessel.

    Some times a pressure differential valve is installed from the between the compressor discharge and the receiver. This valve opens when the receiver pressure drops thereby pressurizing the receiver to a pressure = condensing pressure -differential pressure. This is done to assure that a minimum delta P will exist at the TXV.

  13. #13
    Join Date
    Sep 2010
    Location
    Australia
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: Receiver Design

    yea, I'm really confused, that is exactly why we put a receiver there as an accumulator tank. I just dont know why my lecturer assigned me to do PID on the condenser before this receiver and this receiver tank.. And the condenser in my assignment is air cooled too.. So, there is really nothing to be controlled I guess.. Maybe I'll draw the piping there. so we dont even need a control valve?
    do u think a pressure relief valve would be enough for that tank? I dont think level control or temperature control is necessary

    Thanks a lot for the advice

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Receiver Design

    As previously said, you do not control the level in the receiver.

    The refrigerant is simply stored there, in various quantities, while the system is running.

    The condenser generates the liquid from hot vapour and it passes to the receiver for use later in the cooling process.

    Air cooled condenser then perhaps add a fan speed control to stabilise the pressures?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Sep 2010
    Location
    Australia
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: Receiver Design

    alright, thank you very much for the helps!

Similar Threads

  1. "Unstable" Rack Receiver Liquid Level
    By chweber in forum Commercial
    Replies: 3
    Last Post: 09-02-2009, 08:58 AM
  2. Receiver! Needed or not
    By The MG Pony in forum Fundamentals
    Replies: 4
    Last Post: 22-08-2007, 08:51 PM
  3. Replies: 31
    Last Post: 28-11-2006, 10:32 PM
  4. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •