    haccp function - carel



    hi, i have problem with mastercella MD33D5EB00. I programmed everything I needed in plantvisor including the haccp function. So there was a power loss and the mastercella detected high temperature (HI) and HA also triggered because of HACCP. I deleted the HI but cant delete the HA alarm, even with acknowledge, delete. I also tried to delete it manually on mastercella but i cant access the haccp menu. I was using the instructions from datasheet for mastercella.
    And after some time I discovered that version of mastercella i bought doesnt have an haccp function, but on my mastercella haccp leds are blinking so as HA state of alarm.

    any help?
    Attached Images Attached Images



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: haccp function - carel

    Parameter to: reset HACCP alarm
    If set to 1, this parameter indicates the activation of an HACCP. Setting
    it to 0 resets the alarm.
    In the LARGE terminals, the same function is achieved by pressing the
    HACCP button for 5 s.

  3. #3
    Join Date
    May 2010
    Location
    Bosnia and Herzegovina
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: haccp function - carel

    Problem is I cant access the menu of HACCP and I cant read the HA alarm (date, duration). Where to set 0?

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: haccp function - carel

    http://www.carel.com/carelcom/web/do.../030220441.pdf

    I have just turned to Carel's cite - this instruction ? Read it more carefully please.
    Last edited by Yuri B.; 06-09-2010 at 07:10 PM.

  5. #5
    Join Date
    May 2010
    Location
    Bosnia and Herzegovina
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: haccp function - carel

    HA is blinking. So I press: HACCP button more than 5 seconds --> NOTHING IS HAPENNING

    I triedalso: DOWN/DEF +SET: if
    pressed together for more than 5 seconds, displays a sub-menu used to access the parameters relating to the HACCP alarms (‘HA’, ’HAn’,
    ’HF’, ’HFn’).

    and UP + SET more than 5 sec...

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: haccp function - carel

    Did you f---ing read what I wrote? Parameter t0. You have to change paramter t0 to 0.

  7. #7
    Join Date
    May 2010
    Location
    Bosnia and Herzegovina
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: haccp function - carel

    Oh I didnt realized that "to" is actually "t0". Tnx I ll try that.

  8. #8
    Join Date
    May 2010
    Location
    Bosnia and Herzegovina
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: haccp function - carel

    Quote Originally Posted by dark_jackal7 View Post
    Oh I didnt realized that "to" is actually "t0". Tnx I ll try that.
    and where do you find this parameter? i`m trying to find it in datasheet but there is no t0 parameter. ?

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: haccp function - carel

    between parameter St and parameter tu. It's actually to and not t0.

  10. #10
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: haccp function - carel

    It seems I have given the link to wrong manual, look up this one:

    http://www.carel.com/carelcom/web/do.../030221396.pdf

    page 34.

  11. #11
    Join Date
    May 2010
    Location
    Bosnia and Herzegovina
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: haccp function - carel

    in the first post there is a picture of mastercella I`ve got. It is MD33.... --> new mastercellas line. And the first pdf you put is the one I have to use. On the picture it is highlighted full code of mastercella and on the picture is shown that I havent got the HACCP function at all. But I activated it somehow. And its blinking. I tried all the methods of deleting it but I didnt have any success. I tried also to set parameter "HACCP delay" to 0 but nothing. So if you really want to help just try to understand the problem and you dont have to put all those pdfs because I have them all.
    Thanks.

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: haccp function - carel

    Your unit definitely has got HACCP installed.
    Did you try what I wrote, or are you just whining like a little girl about what we have to do to help you?

  13. #13
    Join Date
    May 2010
    Location
    Bosnia and Herzegovina
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: haccp function - carel

    open the first pdf file that Yuri sent, go to page 56 and find that "to" parameter, I cant. And I`m not whining see my last post and that big smile.

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: haccp function - carel

    Hey, smart ass, why don't you just do what you are told. Enter the programming mode and look for parameter to.
    I understand you don't find it in Yuri's manual, but ...you know... I don't give a **** about it.
    Either do it, or **** it.

  15. #15
    sarah ryan's Avatar
    sarah ryan Guest

    Re: haccp function - carel

    Hi there,

    I think you have to take all the information about the HACCP before doing anything.

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: haccp function - carel

    No Nickers you are a character, you obviously have red hair and a short fuse. I love reading your comments and posts.

  17. #17
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: haccp function - carel

    Quote Originally Posted by Magoo View Post
    No Nickers you are a character, you obviously have red hair and a short fuse. I love reading your comments and posts.
    I have neither.
    But you see, no reply from the poster since september. You can bet he found the parameter he was looking for. There are times men needs to be treated as animals.

Similar Threads

  1. Carel / Zanotti setup sheet required
    By Andy W in forum Commercial
    Replies: 2
    Last Post: 05-03-2010, 12:07 PM
  2. Carel electronics - reliability?
    By desA in forum Electrical
    Replies: 24
    Last Post: 04-12-2009, 01:35 PM
  3. carel controller hidden reset button
    By 123-steve909 in forum Commercial
    Replies: 1
    Last Post: 01-06-2009, 09:54 PM
  4. Carel temperature controller issues
    By tegwin in forum Electrical
    Replies: 10
    Last Post: 30-01-2008, 03:10 PM
  5. carel ir33 controllers
    By fowlie in forum Supermarket Refrigeration
    Replies: 11
    Last Post: 17-12-2007, 07:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •