Multi City
Im having a problem with a multi city hocked up to four fan coil unit.Out of four three indoors are cooling an the fourth is only blowing room tempreature air .Have changed all the indoor sensors and still no cooling.Has anybody come across this???Any solutions.
-
01-09-2010, 11:13 PM #2
Re: Multi City
The fourth unit has a fault with it somewhere.
Expansion valve perhaps.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
02-09-2010, 08:33 AM #3
Re: Multi City
have you worked on this type of system before its running on r407 and the expansion valves are screwed on not clip.we tried adjusting the valve both manually an through the Mitsubishi maintenance tool.With no change in tempreature???
-
02-09-2010, 10:02 PM #4
Re: Multi City
do you have done a check up whit the service tool and is the outdoor-unit recognizing all 4 units?
are the given parameters ok?
what are the sensors telling you?
-
03-09-2010, 08:53 PM #5
Re: Multi City
Y series heat pump system
No 4 unit has fault with LEV valve , indoor circuit board or blocked liquid line strainer.
R2 heat recovery system
As above & or also incorrect branch address setting for BC port connection.
Similar Threads
-
RS44 R424a in City Multi
By Collie in forum RefrigerantsReplies: 2Last Post: 22-07-2010, 05:56 PM -
City Multi Undersized
By MOVHVAC in forum Air ConditioningReplies: 3Last Post: 20-07-2010, 06:46 PM -
City Multi Faults
By Collie in forum Air ConditioningReplies: 2Last Post: 22-06-2010, 06:13 PM -
City Multi - Inverter Speed / Noisy Check Valve
By Contactor in forum Air ConditioningReplies: 2Last Post: 22-04-2009, 02:49 AM -
Need input on City Multi
By TDfromNY in forum Air ConditioningReplies: 4Last Post: 09-06-2006, 03:31 AM