    Im having a problem with a multi city hocked up to four fan coil unit.Out of four three indoors are cooling an the fourth is only blowing room tempreature air .Have changed all the indoor sensors and still no cooling.Has anybody come across this???Any solutions.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Multi City

    The fourth unit has a fault with it somewhere.

    Expansion valve perhaps.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    spikybm's Avatar
    spikybm Guest

    Re: Multi City

    have you worked on this type of system before its running on r407 and the expansion valves are screwed on not clip.we tried adjusting the valve both manually an through the Mitsubishi maintenance tool.With no change in tempreature???

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Multi City

    do you have done a check up whit the service tool and is the outdoor-unit recognizing all 4 units?
    are the given parameters ok?
    what are the sensors telling you?

  5. #5
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Multi City

    Y series heat pump system
    No 4 unit has fault with LEV valve , indoor circuit board or blocked liquid line strainer.
    R2 heat recovery system
    As above & or also incorrect branch address setting for BC port connection.

Similar Threads

  1. RS44 R424a in City Multi
    By Collie in forum Refrigerants
    Replies: 2
    Last Post: 22-07-2010, 05:56 PM
  2. City Multi Undersized
    By MOVHVAC in forum Air Conditioning
    Replies: 3
    Last Post: 20-07-2010, 06:46 PM
  3. City Multi Faults
    By Collie in forum Air Conditioning
    Replies: 2
    Last Post: 22-06-2010, 06:13 PM
  4. City Multi - Inverter Speed / Noisy Check Valve
    By Contactor in forum Air Conditioning
    Replies: 2
    Last Post: 22-04-2009, 02:49 AM
  5. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •