    Water chilling/heating



    Guys

    I'm just an average tinkerer and looking for some input.

    I have 2x300 litre water tanks and was thinking of rigging a heat pump (modified 8000BTU aircon unit) between the two. Heat exchanger in each. One tank for cold water and one for hot.

    Regardless of the size of the pump, isulation issues etc, what would the theoretical achievable temperature difference be between the two tanks?

    Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Water chilling/heating

    A difficult question to answer as you do not give a time span, or if the water flows from 1 tank to the other, or is on a recirculation basis. If you had a start and finish temperature, water moving from one point to the other, and a time span, then the equation would be simple.

    What you are asking is - how much energy can a 2.34kW heat pump add to 2 cylinders of water?

    But then you are saying (I think) that one will remain cold while the other becomes hot due to the energy input.

    Can you refine your question?

  3. #3
    blug's Avatar
    blug Guest

    Re: Water chilling/heating

    Hi Frank

    Thanks for the speedy response.

    The two tanks are not interconnected. For the purpose of this exersize consider them sealed.
    I am not concerned about time either. What I am trying to establish is if I leave it running for long enough, what will the temperature difference be between the two tanks.
    If both start at 30C and I am trying to get a 60C differential using 2.34kW, is it achievable?


    It might sound a pointless question, but I have worked with peltiers (not on this scaleof course) and you are stuck with an envelope of 20-30C. If one tank reaches 20C and the other 50C, thats it, no more.

    I have not worked with pumped gas heat exchanging yet and I was hoping one could achieve >60C differential.

    Hope this makes more sense.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Water chilling/heating

    In a refrigeration cycle, depending on the actual refrigerant used, the max differential temperature between the heat sink and heat source is an input data. Theoretically, you could achieve a heat source temperature very close to freezing, and a heat sink up to 80°C.
    The capacity of the heat pump just defines the time it takes to achieve your goal.
    Basicly a 1kW heat pump or 50kW pump can achieve the same result, the latter of which in a 1/50th of the time.

  5. #5
    blug's Avatar
    blug Guest

    Re: Water chilling/heating

    Thats the answer I was looking for. Many thanks

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  3. Modifying aricond. for heating, cooling and hot water
    By kimusabi in forum Technical Discussions
    Replies: 3
    Last Post: 10-10-2008, 07:28 AM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •