    open plan air con



    hey guys im working in a office building with big open plan rooms i have set the dials 19 cooling 20 heating but its coming outat about 16 deg so i turn it up to 21 cooling 22 heating and its coming out 27 degrees im unfamiliar with theses air handling units and the temp seems to fluxuate alot anyway could this be summin to do with sensors in return ducts maybe the sensors are old and not working properly i just cant get the right temp further too that one of the smaller rooms runs of the thermostat in the open plan and as a result is always much warmer or colder any advice theses people are driving me crazy



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: open plan air con

    hi andy , tell me is it the millenium stadium you are looking after? if it is , then if you shut the roof you may get a better result , all the best < only kidding < sedgy

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: open plan air con

    Are you saying that the temperature set point on the thermostat is 19C and the air coming out of the air conditioner is 16C?

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: open plan air con

    Hi Andy
    I think the heating setpoint should be lower than the heating setpoint. Something like cooling 23°C and heating 21°C. So as if the sensor reads lower than 21 the heating will come on and above 23 the cooling will come on.

Similar Threads

  1. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 08:11 AM
  2. TXV/Check Valve Stuck Open
    By tesla500 in forum Heat Pumps
    Replies: 4
    Last Post: 27-10-2010, 01:31 AM
  3. Hinari and how far to open valves
    By stryker in forum Air Conditioning
    Replies: 6
    Last Post: 14-04-2008, 01:47 AM
  4. Blamed for open freezer door
    By RichTea in forum Domestic
    Replies: 17
    Last Post: 22-11-2006, 07:43 PM
  5. Open Type Compressors
    By shogun7 in forum Air Conditioning
    Replies: 1
    Last Post: 07-01-2005, 09:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •