    Check valve selection



    There is interesting problem of check valve selection in parallel working compressors. I select check valve for liquid line (condenser/receiver) for total compressors capacity, but when some compressors not work there are low opening degree and there is a risk of instabillity of working, because the flow of refrigerant is to small to open this valve. Velosity in thise pipe must be no more then 0.5 m/s, if I select more smaller valve then it will open on minimum compressors capasity but on maximum capasity velosity of liquid will be 1.4 m/s. Could you tell me how can I solve this problem?


    In some places will have to think ...

  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Check valve selection

    Many check valves start opens at 0,1 bar or less. So in this particular case if you have a column of 1 m » 2 m of liquid (depending of the refrigerant density) between condenser outlet and receiver it will no problem.
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Check valve selection

    Quote Originally Posted by Sandro Baptista View Post
    Many check valves start opens at 0,1 bar or less. So in this particular case if you have a column of 1 m » 2 m of liquid (depending of the refrigerant density) between condenser outlet and receiver it will no problem.
    Good. What will you do when in the same situation check valve will situate on discharge pipe?
    In some places will have to think ...

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Check valve selection

    Do you mean on the discharge pipe of each compressor?
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Check valve selection

    Quote Originally Posted by Sandro Baptista View Post
    Do you mean on the discharge pipe of each compressor?
    No, one for all compressors, for example after general oil separator.
    In some places will have to think ...

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Check valve selection

    In that case is more complicated...but depending the number of compressors and/or its capacity stage may have an unique valve that accept as minimum capacity 15-20% without generate high pressure drop ate 100%.

    If there is only one rack with one general oil separator I don't see the necessity of install check valve albeit many plants have it.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Check valve selection

    Quote Originally Posted by Sandro Baptista View Post
    If there is only one rack with one general oil separator I don't see the necessity of install check valve albeit many plants have it.
    Check valve on discharge pipe protect from condensation refregirant in oil separator when unit not work in case with air condenser when ambient temperature is high then temperature in the compressor's room.
    In some places will have to think ...

  8. #8
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Check valve selection

    The refrigerant can be evaporated by electric heat around the oil tank; or shut off by electric valve the oil return to the oil thank and heating the oil separator or give a time to open the EVR to oil tank after the compressor working about 10 min.
    To make progress is never good enough, I want to do better and better and better

  9. #9
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Check valve selection

    Quote Originally Posted by Sandro Baptista View Post
    The refrigerant can be evaporated by electric heat around the oil tank;
    You are right, but not all oil separators have electric heat.
    In some places will have to think ...

  10. #10
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Check valve selection

    You can buy it separate from the oil separator. It is an electric strap that is put around the oil separator. It is sold on PECOMARK, DISCOLIS, or other suppliers.

    Or use a timer as I explain above
    To make progress is never good enough, I want to do better and better and better

  11. #11
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Check valve selection

    Have you looked at Danfoss check valves as I know your predicament for selection can be difficult to avoid fluttering.
    On industrial we use duo check valves which handle your circumstances but of course you may not want flanges .

  12. #12
    Join Date
    Sep 2009
    Location
    Australia
    Posts
    41
    Rep Power
    0

    Re: Check valve selection

    How sensible it is to have one check valve in the discharge line for parellel compressor operation? Won't it hamper the compressor capacity?

    regards
    BR

  13. #13
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Check valve selection

    I'd suggest using one check-valve per compressor - correctly sized to suit compressor delivery.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. daikin vrv II not heating
    By DoD in forum Heat Pumps
    Replies: 3
    Last Post: 17-01-2010, 05:23 PM
  2. SullAir/Jordan Valve
    By jaysephus in forum Industrial Compressors
    Replies: 42
    Last Post: 12-01-2010, 04:29 AM
  3. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  4. Replies: 2
    Last Post: 06-02-2009, 07:35 PM
  5. Double check needed
    By Latte in forum Trouble Shooting
    Replies: 14
    Last Post: 11-08-2004, 12:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •