    Flooded Systems



    Was introduced to a huge water chiller recently ,the system is a lot larger than I normally work with but I found it fasinating.It was a flooded system ?? Please can someone explain this, it had a very large suction accumulator and a flow con valve.They have a problem from time to time where liquid gets trapped in the suction accumulator and the only way to get it out is to add more gas then recover it again????This does not sound correct, why would this happen,what is the advantages with a flooded system.


    Regards Bernard



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flooded Systems

    A flooded system provides a more constant (if that is the right word?) cooling surface as the refrigerant is not in a superheated state when in contact with the secondary cooling medium.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2005
    Location
    SOMEWHERE IN THE PLANET
    Age
    46
    Posts
    67
    Rep Power
    19

    Re: Flooded Systems

    The liquid recover system seems not econmical but simple. The hot gas enter the accumulator to boil the liquid. if so, this is the cheapest way to solve the problem. sometimes people will install a liquid pump or another tank to pipe the liquid to high side. And maybe you can lower the level of the chiller to to get some superheat and see what happens.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Flooded Systems

    Quote Originally Posted by JERRYCOOL
    .. The hot gas enter the accumulator to boil the liquid.
    This beed some explanation for me.
    I always thought that the return mix of gas and liquid came into the accumulator.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jul 2004
    Location
    england
    Age
    52
    Posts
    64
    Rep Power
    20

    Re: Flooded Systems

    Might need a enconomizer fitted after expansion valve. What make of chiller are you working on?

  6. #6
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Flooded Systems

    Sounds like you have an economizer with a hi presure float thats 'Hanging up If this is an air conditioning chiller I don't see a need for an accumulator.

  7. #7
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Flooded Systems

    Flooded systems are generally used in larger systems where you can not get a thermal expansion valve sized large enough. Also with large DX units you do get into problems with liquid distribution in the tubes. Another case where you would use a flooded exchanger is certain fluids do better with them being cooled in the tubes. Such as fluids which are prone to high fouling rates. Also, corrosive fluids where it is cheaper to build an exchanger with stainless steel tubes, tube sheet and channel as opposed to an expensive stainless steel shell.

    Is the flooded system you are looking at one with the liquid in the shell of the evaporator and is it controlled by a high side float as in a critically charged system or is it low side float or orifice plate controlled? Is it on a water chiller or on a lower temperature industrial process system.

    My primary concern is that in a properly designed flooded system the suction accumulator should run dry and is there as a safety device to protect the compressor from process upsets and liquid slugs. If it routinely gets flooded with liquid, they are either creating a process upset and slopping over liquid, the evaporator is not properly designed or they have the liquid level too high.

    Another type of stem refereed to as "flooded" is a coil or unit cooler that is fed by a gravity drum (or thermosiphon drum). These are typically used in larger industrial cooled warehouses. In these, the drum runs wet and acts as a suction accumulator as well as a liquid supply drum.

    When I design a system with a suction accumulator, I generally take the warm condensed liquid through a "boil-out coil" in the bottom of the accumulator. This supplies a small heat source to get the refrigerant to boil out in the event of a liquid flood over.

    I do hope that they have an oil recovery system attached to the accumulator to get oil back to the compressor (probably will not on a centrifugal compressor).

    The ASHRAE Handbook has a good explanation of flooded evaporators. Another book that is a good source of refrigeration data and design is Refrigeration Fundamentals by Wilhelm Stoecker.

    Ken

  8. #8
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Smile Re: Flooded Systems

    Attachment is a sketch from ASHRAE handbook for your ref.

  9. #9
    ferretman's Avatar
    ferretman Guest

    Re: Flooded Systems

    Dear Bernard

    The reason for the large suction accumlator is that the system as you know is flooded,any liquid that does not boil off through heat transfer then returns to the accumlator,inside the accumlator passes the liquid line the heat from the liquid line boils off the returned liquid from the evap then the vapour is then drawn off the top to the compressor.the system will run with a high level switch on the accumlator so if the level raises the switch will make and drop out the compressor to stop any damage.If this happens then liquid will need to be decanted from the accumlator and the problem repaired i.e solinoid valve passing.Hope this helps.

  10. #10
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Flooded Systems

    why can't upload,try again.
    Last edited by Lc_shi; 10-04-2007 at 09:39 AM.

Similar Threads

  1. contaminants in ammonia systems
    By Johnny Rod in forum Refrigerants
    Replies: 29
    Last Post: 17-10-2011, 05:26 PM
  2. flooded evaporator in screw chiller
    By Lc_shi in forum Technical Discussions
    Replies: 25
    Last Post: 05-07-2010, 05:37 AM
  3. My local Apprentice Training Classes
    By shogun7 in forum Training
    Replies: 12
    Last Post: 17-03-2007, 03:10 PM
  4. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Replies: 15
    Last Post: 21-04-2006, 10:02 PM
  5. someone please help!
    By dormy in forum Fundamentals
    Replies: 14
    Last Post: 10-01-2005, 08:43 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •