    When a pumpdown did NOT!



    Working on an older container not reaching 2c, had been running on R134a and the copeland semi cycling on L.P. Closed off reciever when i found 3/8 drier cool on outlet. The distance between reciever and drier about 4 foot. Cycled Lp several times manually untill compound gauge stopped rising then undid drier flare on the outlet side, great, then started unscrewing flare on inlet and contaminated "chocolate" coloured oil oozed out. Wriggled the nut then BANG WHOOSH! When i could see again the flare was still on the drier and the contents saturated me from a to b. Completed the job, kept the faulty flare and drove home( 30mins) in my jocks.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: When a pumpdown did NOT!

    Quote Originally Posted by mikeref View Post
    Working on an older container not reaching 2c, had been running on R134a and the copeland semi cycling on L.P. Closed off reciever when i found 3/8 drier cool on outlet. The distance between reciever and drier about 4 foot. Cycled Lp several times manually untill compound gauge stopped rising then undid drier flare on the outlet side, great, then started unscrewing flare on inlet and contaminated "chocolate" coloured oil oozed out. Wriggled the nut then BANG WHOOSH! When i could see again the flare was still on the drier and the contents saturated me from a to b. Completed the job, kept the faulty flare and drove home( 30mins) in my jocks.
    Nice to notice an "Old Hand" admitting that things still go wrong.
    I bet that oil smelt "sweet" on your clothes.
    Nice one Grizzly.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: When a pumpdown did NOT!

    Bet your wife loved having to wash the oily clothes.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: When a pumpdown did NOT!

    lol, i once knew an apprentice who was changing relief valves on a chiller and took the wrong one off 3/4 bore off the oil sep whilst system was running it took some getting back on

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: When a pumpdown did NOT!

    Messing around with an old removed drier that had the plastic caps on.

    Idly removed one of the caps which promptly blew off half way undone due to the pressure inside.

    Problem was it injected my forearm with all the crap that was inside the drier. Looked like my arm had been painted with a black stipple brush, but below the skin. Took a week before it started coming out of the skin again.

    Didn't half hurt too.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: When a pumpdown did NOT!

    Quote Originally Posted by Brian_UK View Post
    But back to the thread topic....OR NOT - Hey Ho.
    you looking at the wrong thread Brian?

    EDIT: Thanks James, wondered why I couldn't see elsewhere, must be dummy day.... Cheers Brian
    Last edited by Brian_UK; 01-09-2010 at 11:03 PM. Reason: There are some idiots about.....Brian

  7. #7
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: When a pumpdown did NOT!

    good thing you were wearing jocks bet the truckies would still be double looking
    mmm to beer or not to beer...........lets drink breakfast

  8. #8
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: When a pumpdown did NOT!

    Still do the work there but carry plenty of rags and spare clothes now.. the workwear of that day didn't survive.

Similar Threads

  1. Pumpdown of Trane Chiller RTHB 450
    By skygod007 in forum Trouble Shooting
    Replies: 1
    Last Post: 25-07-2010, 02:11 PM
  2. medium temp pumpdown vs no pump down
    By Harrison in forum Commercial
    Replies: 4
    Last Post: 04-02-2009, 01:20 PM
  3. Replies: 8
    Last Post: 18-03-2007, 01:24 PM
  4. setting LP control on pumpdown system.
    By Temprite in forum Commercial
    Replies: 9
    Last Post: 02-01-2007, 10:33 PM
  5. EXV and Pumpdown
    By bersaga in forum Technical Speculations
    Replies: 12
    Last Post: 31-08-2005, 06:28 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •