    Condensing Units



    HEY GUYS,
    PLS BEAR WITH MY KNOWLEDGE OF A NOVICE IN REFRIGERATION SYSTEMS, WE ARE UNDERTAKING THE MANUFACTURING OF A NEW TEST PEICE AND DO NOT KNOW HOW TO GO ABOUT SELECTING A CONDENSING UNIT. I HAVE THE OPENING SIZE FOR THE REFRIGERATOR(24"X48"x22"), WE PLAN TO USE 404A AS THE REFRIGERANT, THE AMBIENT TEMPERATURE IS 86F-100F, AND THE TEMPERATURE WE NEED TO MAINTAIN INSIDE THE REFRIGERATOR IS 34F-40F.
    I WOULD REALLY APPRECIATE ANY INFORMATION YOU CAN GIVE ME AS TO HOW TOO CALCULATE THE BTU/HR CAPACITY AND THUS ENABLING ME TOO CHOOSE THE RIGHT CONDENSING UNIT AND COMPRESSOR.
    THANK YOU
    ASH



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Condensing Units

    What is the purpose of this 'thing', this test peice?
    What goods are brought in it?
    Entering temperature?
    Final required temperature?
    Mass/hour?
    Required cooling time?
    Humidity level?
    Doors and size?
    How any times will they open?
    Other heat producing equipment inside?
    .....

    Why R404a and why a condensing unit AND a compressor?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    SERGIO ROD's Avatar
    SERGIO ROD Guest

    Re: Condensing Units

    For What I Know R-404a Is For Freezers, Ice Machines, Margarita Machines An So On..., You Can Use A Condensing Unit That Uses R-134a For Medium Temp, The Compresor Is Already Included In A Condensing Unit..., All The Questions Peter Is Asking Are Very Important Facts To Consider, Because They Are Variables That Will Affect And Determine The Right Choice Of The Condensing Unit You Will Use... Do You Know The Size Of The Evaporator That Is In That Refrigerator Or Are You Gonna Use A New One...? Cubic feet...? the more information you can provide the more accurate the help will be....
    Last edited by SERGIO ROD; 20-06-2005 at 11:09 PM.

  4. #4
    DHASHU's Avatar
    DHASHU Guest

    Re: Condensing Units

    1:What is the purpose of this 'thing', this test peice?
    IT IS TO BE USED AS A REACH IN COOLER FOR FOOD PRODUCTS IN A CAFETERIA.
    What goods are brought in it?
    STUFF LIKE SALADS ETC
    Entering temperature?
    38F
    Final required temperature?
    ANYWHERE IN BETWEEN 34F AND 40F
    Mass/hour?
    N/A
    Required cooling time?
    VARIES
    Humidity level?
    EQUIVALENT TO FOOD PRODUCES
    Doors and size?
    2 SETS OF SLIDIDNG DOORS 35"x20"
    DOORS ARE INSULATED
    How any times will they open?
    CANNOT BE ACCOUNTED
    Other heat producing equipment inside?
    NONE
    .....
    THANKS GUYS
    ASH
    Why R404a and why a condensing unit AND a compressor?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Condensing Units

    PLS BEAR WITH MY KNOWLEDGE OF A NOVICE IN REFRIGERATION SYSTEMS, WE ARE UNDERTAKING THE MANUFACTURING OF A NEW TEST PEICE AND DO NOT KNOW HOW TO GO ABOUT SELECTING A CONDENSING UNIT
    If you want to avoid problems later on I would honestly suggest that you employ an refrigeration design engineer at this stage.

    There are many variables that you need to consider in the design, it is not as simple as selecting a condensing unit.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Condensing Units

    Somewhat same question: I'm a novice in designing airliners.
    I want to make an airliner which can fly from Belgium to Russia, non-stop, carry 50 persons and fly at FL350.
    I want as much information as possible how to design the jet-engines.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Condensing Units

    On the following parameters, I have come up with the following system for your project
    For a cabinet temperature of 35/40*F and a volume of ~16 cu ft, a load of 1300btu/hr is given in “Heatcraft” calculations also the (2) insulated sliding glass doors are equal to about 1000btu/hr, all is based on a 16 hour run time total ~2300btu /hr. If the doors are not insulated then you need to add 1000btu/hr. So with the following in mind, I feel that the following condensing unit should do a proper job.

    Copeland model# ASE20C4E-IAA
    MT: Medium Temperature Rating Conditions
    Refrigerant: 404A 40 Return Gas (F)
    Voltage: IAA 115-1-60 0 Sub Cool (F)
    20 Compressor Super Heat (F) 95 Ambient Temperature (F)
    Production Status: Available for sale to all U.S. customers. Please check with your local Copeland representative for international availability.
    Evap Temp (F) = 20 RLA = 5.2
    Cond Temp (F) = 110 Half Winding RLA =
    Capacity (Btu/hr) = 2370 LoLRA =
    Power (Watts) = 451 HiLRA = 26.5
    Current (Amps) = 5.3 Half Winding LRA =
    Mass Flow (Ibs/hr) = 52 Max Operating Current =
    EER (Btu/W-hr) = 5.3
    Isentropic Efficiency = 42.8
    Evaporator Superheat (F) = 20, Net Refrig Effect (Btu/hr) = 2370
    If this is not to your satisfaction, then may I suggest you talk to the copeland people at the following
    http://www.copeland-corp.com/cp_rf/cp_rf_.htm

  8. #8
    Join Date
    Jan 2004
    Location
    Quebec,Canada
    Posts
    10
    Rep Power
    0

    Re: Condensing Units

    The total refrigeration load is the total of the following “load segments”:

    • Transmission Load - heat gain through walls, floors and ceilings.
    • Air Change Load - heat gain associated with air entering the refrigerated space, either by infiltration or ventilation.
    • Product Load - heat removed from and produced by products brought into and stored in the refrigerated space.
    • Internal Load - heat produced by internal sources such as
    lights, electric motors, and people working in the space.


    ....not as simple as you thought

  9. #9
    DHASHU's Avatar
    DHASHU Guest

    Re: Condensing Units

    thanks guys,
    the information has been extremely helpful. shall let you all know if the prototype functions.
    ASH

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Condensing Units

    Never thought it could be that simple.
    Why on earth I ever read al those books?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: Condensing Units

    I'm with you peter. think I'll just get all my refrig students to log on here..be easier than than having to teach them all the theory
    100% is possible 100% of the time

  12. #12
    DHASHU's Avatar
    DHASHU Guest

    Re: Condensing Units

    Hey Peter,
    Well I Dont Know If That Was Sarcastic Or What, But I Did Have To Read A Lot Of Books Just To Figure Out What U Guys Were Saying.
    Thanks
    Ash

  13. #13
    Join Date
    Jun 2005
    Location
    Madison
    Age
    61
    Posts
    32
    Rep Power
    0

    Re: Condensing Units

    I do agree with Peter. You had better to hire a refrigeration engineer to design it for you. At least you should ask someone to calculate the heat load for you. The information you gave is not enough to determine the heat load. At this point, it is impossible to select the right condensing unit for you.

    There is one thing I want to piont out. If you want to keep the food temperature between 34F to 40F, I feel R134a is better than R404a.

  14. #14
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    21

    Re: Condensing Units

    first why r404 at the amb you are running your head is going to be out of sight. use a drop in i dont know where you are so dont know what is sold here i would use r22. size would be hard to tell not knowing how the cooler was built. Here i would use a 1500 BTU coil and match compressor at 20 deg sst.
    wesmax
    Wes Maxfield

Similar Threads

  1. Lifting Condensing units!
    By daddymac in forum Air Conditioning
    Replies: 35
    Last Post: 09-02-2009, 11:11 AM
  2. top exit condensing units
    By old gas bottle in forum Industrial
    Replies: 4
    Last Post: 10-10-2006, 03:03 AM
  3. Sizeing condensing units
    By Latte in forum Commercial
    Replies: 4
    Last Post: 25-11-2004, 09:26 PM
  4. Compressor for condensing units
    By ah_Keng in forum Commercial
    Replies: 1
    Last Post: 11-12-2003, 01:39 PM
  5. Parellel Condensing Units
    By bersaga in forum Technical Speculations
    Replies: 9
    Last Post: 08-05-2003, 02:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •