    Aug 2010
    Malta
    11
    R22 Chargin pressure
    HI guys
    Please can some one tell me, what is the charging pressure range at the suction site and and the discard pressure range for a LBP R22 hermetic compressor
    And what conditions determine to use LBP and not HBP compressors,
    And internally what is the difference between LBP and HBP
    Marco
    Jun 2009
    North East England
    712
    Re: R22 Chargin pressure
    pressure is merley a side effect of temperature which is what you need to look at the temperature will vary from system to systemfor instance if you had cold room you wanted to be at 0 degrees c you would be looking at a saturated suction temp of -5/-8 degrees c using a comparator wolud give you the equvilent preesure for this temperature
    Aug 2010
    Malta
    11
    Hi James
    Please note that I have little knowledge in refrigeration !!
    I have a 1/2 copper pipe coiled inside a water tank to cool the water from 30 to 14 degree Celsius and am using a LBP 12 cc 404a compressor but am using R 22 instead. With this information that I am give in you, Is it possible that you tell me what pressure I should give at the suction please ?
    Marco
    Oct 2008
    mallorca, spain,
    75
    768
    hi marco , have you read about R 22 ? the industry is trying to cut down its use , it is said to be detromental to the atmosphear, you say the comp, is for 404a why not use that?
    Aug 2010
    Malta
    11
    Hi Sedgy
    Yes I know that they are phasing out R22 . am using R22 instead of 404 because I still have left some R22
    Marco
    3,853
    Quote Originally Posted by maltamarco View Post
    HI guys
    Marco
    There isn't a correct pressure, it depends on the evaporator load and condensers ability to reject the heat gained in the evap and compressor.
    LBP are found in freezer low temp systems (think low suction pressure)
    HBP are found in chiller and air con systems (think high suction pressure)
    The two types of compressor will have different displacements for the same motor power, a LBP comp may be overloaded in HBP applications.
    Jon
    Oct 2008
    mallorca, spain,
    75
    768
    hi marco , so you are using R22 cos you < or your firm < has someR22< not because its killing our atmosphear but because your gettin it free , I am glad most of the fridge engineers thinkabout the world befofe themselfs
    cos time is running out for YOU , and your kids , all the best - see you on the other side, not down there thats where they burn the fosgeen
    Jul 2010
    New Zealand
    11
    R22 is not a L Temp refrigerant, to run it.....and it will run at medium temp......in a 404A LT compressor you are going to need a crankcase pressure regulator to protect the compressor motor which will chop severly into your capacity......LT with R22 is courting disaster with burnt out discharge valves due to high discharge temperatures, the only real way to use R22 as low temp is via a type3 or bigger Bitzer with a watercooled head. as for temperature/ gauge pressure.......well that depends on a bundle of factors you could begin with 230 over 60 though that also depends on your expansion device...........enjoy.......
    May 2008
    Malta
    68
    67
    The difference between LBP and HBP is in the design of the compressor.LBP compressors are for freezers and high for fridges the motor size will be difference and very often LBP compressors will have an oil cooler as low suction pressure require more cooling.
  1. Evaporating pressure valve
    By civic9696 in forum Technical Discussions
    Last Post: 26-08-2010, 05:20 AM
  2. NVQ 3 online test
    By Burrah Boy in forum Training
    Last Post: 28-10-2009, 08:35 PM
  3. Effect of inverter on Pressure Ratio
    By GIB in forum Air Conditioning
    Last Post: 03-10-2009, 01:54 PM
  4. How can I reduce evaporator pressure?
    By mansari in forum Fundamentals
    Last Post: 05-09-2009, 01:59 AM
  5. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Last Post: 06-12-2002, 05:11 PM
Tags for this Thread