27-08-2010, 11:37 AM #1
Refrigeration Question
what is the cause of discharge line high pressure? please answer ASAP thank you.
-
27-08-2010, 11:54 AM #2
Re: Refrigeration Question
equipment capacity in quetsion, check the design capacity and selected machine
-
27-08-2010, 12:11 PM #3
Re: Refrigeration Question
this is a refrigerated fishing vessel using hasegawa refrigeration compressor. The condenser tubes and the coils have no leaks. We have no problem at the start of the operation but after two days the operation discharge pressure goes up.What is the problem? Can you help me?
-
27-08-2010, 12:22 PM #4
-
27-08-2010, 12:36 PM #5
Re: Refrigeration Question
yes. And the temperature is normal.
-
27-08-2010, 12:50 PM #6
Re: Refrigeration Question
You have a clogged condenser. Probably algaes or harbour garbage.
-
27-08-2010, 12:56 PM #7
Re: Refrigeration Question
hi lexicon, have you cleaned the sea water inline filter? is thje cargo hold doors sealed most of the day? when was the system last serviced? let us know the outcome,
-
27-08-2010, 01:01 PM #8
Re: Refrigeration Question
We have opened and checked the condenser tubes and it is clean. But still, the discharge pressure is high. We have also set the cut off pressure switch to be able to continue our operation but the pressure still goes up.
-
27-08-2010, 01:03 PM #9
-
27-08-2010, 01:05 PM #10
Re: Refrigeration Question
The filter is clean, but you may still have algaes vegetation in the condenser tube. Did the blast freezer stand by for a long time unattended?
-
27-08-2010, 01:15 PM #11
Re: Refrigeration Question
The boat will go to the port to unload the catch for fifteen days. It will go fishing again after unloading the catch. So the blast freezer is in stand by only for fifteen days. We will open the condenser again tomorrow to double check the tubes if there are still algaes vegetation.
-
27-08-2010, 07:48 PM #12
Re: Refrigeration Question
If your condenser is free and clean, baka may air or non-condensables ka sa system mo Kabayan. Are you using NH^3?,what is your operating suction pressure? or maybe you have restrictions in the condenser water flow or sa high-pressure line from comp. to receiver tank..
<"No one is so smart, they just stay with problems longer and use their imagination">
-
28-08-2010, 05:24 AM #13
Re: Refrigeration Question
No, we are using R22. Thank you very much sa advices mo check ko ulit system namin.
Similar Threads
-
SOS!!!! HOW TO calculate refrigeration system and choose refrigeration Accessori
By ashp in forum Refrigeration BooksReplies: 9Last Post: 30-11-2009, 10:08 AM -
Refrigeration plant Hydro test
By psrao in forum New TechnologiesReplies: 17Last Post: 09-04-2008, 12:05 AM -
new guy in industrial refrigeration
By henry.zhang in forum IndustrialReplies: 7Last Post: 25-03-2008, 09:05 AM -
refrigeration stress
By wellcold in forum Chit Chat & Service StoriesReplies: 4Last Post: 13-12-2001, 03:56 AM