  1. #1
    andersnielsen45's Avatar
    andersnielsen45 Guest

    better COP at winter



    When I hat my theoretical lectures on refrigeration we always set the condenser temperature to about 35 C. This makes sense on a summer day but on a winter day maybe 10 C is enough, resulting in much better COP. My question is:

    • Is it possible to adjust the pressure on the condenser side “on the run” based on outdoor conditions?
    • If yes what do I google to read more about this technique?

    hop you can help
    Anders Østergaard Nielsen (DK)



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: better COP at winter

    Yes, what you are looking for is called floating condensation. The limit is the lowest condensation pressure and highest subcooling for which the evaporator is able to exchange the excess capacity resulting. The excess capacity can easily result in a lowering evaporating pressure for which a low pressure alarm is likely to happen.

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: better COP at winter

    do they not by-pass the low pressure alarm at the condenser, and read the low pressure at the compressor?

    Ice

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: better COP at winter

    There is no such a thing like a low pressure in the condenser....

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: better COP at winter

    I would do the following for R717, as example:

    Condensing pressure set-point: 9 bar (+25ºC saturated temperature) still guarantee a good pressure difference to expansion valves feed the liquid separators. If the discharge pressure tend to be sufficient slower (depend of the differential) the condensing will reduce the ventilation to achieve the set-point.

    On the summer the wet bulb is higher and for design condition at 100% load would achieve +35ºC (12,5 bar).

    At winter the wet bulb is lower and many periods the equilibrium compressors «» condensers will natural be at +25ºC condensing temperature.
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: better COP at winter

    Quote Originally Posted by Sandro Baptista View Post
    I would do the following for R717, as example:

    Condensing pressure set-point: 9 bar (+25ºC saturated temperature) still guarantee a good pressure difference to expansion valves feed the liquid separators. If the discharge pressure tend to be sufficient slower (depend of the differential) the condensing will reduce the ventilation to achieve the set-point.

    On the summer the wet bulb is higher and for design condition at 100% load would achieve +35ºC (12,5 bar).

    At winter the wet bulb is lower and many periods the equilibrium compressors «» condensers will natural be at +25ºC condensing temperature.
    I didn't get about natural equilibrium between compressors and condensers. Can you give us more information?

  7. #7
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: better COP at winter

    Condensing pressure set-point: 9 bar (+25ºC saturated temperature) still guarantee a good pressure difference to expansion valves feed the liquid separators.
    Totaly agree with Sandro Baptista, before reduce condensing pressure you must examine how will work expansion valves.
    In some places will have to think ...

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: better COP at winter

    Quote Originally Posted by Sandro Baptista View Post
    If the discharge pressure tend to be sufficient slower (depend of the differential) the condensing will reduce the ventilation to achieve the set-point.
    That's exactly what he does not want to achieve. He wants the fans at full steam always, to have the lowest possible condensing pressure.

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: better COP at winter

    Quote Originally Posted by NoNickName View Post
    There is no such a thing like a low pressure in the condenser....
    quite wright, never IN but at the condenser. some mount them before the 4way valve, others after. but always around the condenser.

    ice

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: better COP at winter

    That's news to me. As far as I know, the LP switches are in or around or at the suction pipe.

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: better COP at winter

    Just let the condensor pressure drop either use mutiple vales rated at different pressure drops (or dare I say an electronic valve) or just go LPA

  12. #12
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: better COP at winter

    Quote Originally Posted by NoNickName View Post
    That's exactly what he does not want to achieve. He wants the fans at full steam always, to have the lowest possible condensing pressure.
    But in that way it can compromise the liquid feeding and besides that in some cases it can expend more energy because the reduction of discharge pressure is small (when the condensing temperature and the wet bulb are almost the same) and the COP of the compressors already doesn't change significantly. The mechanical power of the fans is proportional to the cube of rpm (N^3).
    To make progress is never good enough, I want to do better and better and better

  13. #13
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: better COP at winter

    Quote Originally Posted by Segei View Post
    I didn't get about natural equilibrium between compressors and condensers. Can you give us more information?
    Segei I was try to say as an example that at a certain wet bulb at winter (low wet bulb temperature) the designed condenser with CT=+35ºC will give a lot of rejection heat so the equilibrium will be the decrease of the condensing temperature to +25ºC, as example.
    To make progress is never good enough, I want to do better and better and better

  14. #14
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: better COP at winter

    We should talk about COPS(system COP). To optimize condensing pressure, total(compressors+condensers) energy use should be minimum. For wet bulb temp. 30C optimum condensing temp. can be 35C. To get 25C condensing pressure, wet bulb should be 20C or lower. However, optimum(minimum total energy use) condensing pressure will be lower at low wet bulb temp. For 10C wet bulb it can be 15C. Usually, a refrigeration plant has several barriers to operate at such low cond. pressure. These barriers are liquid supply(expansion valves), hot gas defrosting, oil carry-over, liquid injection oil cooling and etc. However, every barrier has a solution. I think that this is our job as refrigeration engineers to solve these barriers.

  15. #15
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: better COP at winter

    Quote Originally Posted by Segei View Post
    However, every barrier has a solution. I think that this is our job as refrigeration engineers to solve these barriers.
    Not every barrier...but almost
    In general I agree with you
    To make progress is never good enough, I want to do better and better and better

  16. #16
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: better COP at winter

    Quote Originally Posted by Sandro Baptista View Post
    Not every barrier...but almost
    In general I agree with you
    Tell me a barrier that can't be overcomed.

  17. #17
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: better COP at winter

    Quote Originally Posted by Segei View Post
    Tell me a barrier that can't be overcomed.
    for example liquid injection oil cooling (LIOC system) when you have a evaporating temperature of....-5ºC for example... and you condensing at +15ºC.
    To make progress is never good enough, I want to do better and better and better

  18. #18
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: better COP at winter

    Quote Originally Posted by Sandro Baptista View Post
    for example liquid injection oil cooling (LIOC system) when you have a evaporating temperature of....-5ºC for example... and you condensing at +15ºC.
    Solutions are 2 TEVs, EEV, LPA, maximum load of the compressor to 80-90%(not 100%) and etc. Choose the solution that is the best for your plant.

  19. #19
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: better COP at winter

    okay men...you win...I'm tired to think on another barrier...maybe one day we talk again about this when happen an opportunity.

    Wait...try this barrier: one R717 refrigerant plant without R717 or any other kind of refrigerant...how can it refrigerate??
    To make progress is never good enough, I want to do better and better and better

  20. #20
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: better COP at winter

    Quote Originally Posted by Sandro Baptista View Post
    okay men...you win...I'm tired to think on another barrier...maybe one day we talk again about this when happen an opportunity.

    Wait...try this barrier: one R717 refrigerant plant without R717 or any other kind of refrigerant...how can it refrigerate??
    This is not matter of winning or loosing.
    My point is that energy savings is complicated issue. For many years we were focused on designing plants with minimum capital investments. The goal was to keep required temperature at maximum refrigeration load(design conditions). Surprisingly, even today many engineers estimate energy savings at design conditions. Plant operate at maximum refrigeration load less than 1% of operating time. How to run this plant for the rest 99%? So people start thinking about designing a plant that can operate more efficient during this 99% of operating time. This is just first step. To get maximum energy savings, plant operation should be optimized. It means optimum operating set points should be determined and implemented. Many companies in North America have given this optimization to the operators. They have achieved just partial optimization. In energy savings, it is easy to do first step, but every next step is harder and harder.
    Attached Files Attached Files

  21. #21
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: better COP at winter

    Quote Originally Posted by Segei View Post
    This is not matter of winning or loosing.
    I was joking...it was an "expression".

    Good post Segei.
    To make progress is never good enough, I want to do better and better and better

  22. #22
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: better COP at winter

    Funny enough, cars are operated at their rated power for less than 1% of the time. It didn't take 100 years to realise that, and they are designed for running economy at much less power than their maximum one.
    Yes, time to revise designing criteria of refrigeration and a/c plants.

  23. #23
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: better COP at winter

    For an example, the Danfoss TES2, wit Orifice 6 at TE -10°C, gives 10.26 kW at 16 DP and 8,23 kW at 4Dp.
    So the capacity is very close to each other despites a 12bar DP which is huge.
    What we do: we select for a DP of 4 to 5 and we can drop the HP as low as we want, the TEV will follow, winter and summer. Most of our packs are running this way.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  24. #24
    AlexKram's Avatar
    AlexKram Guest

    Re: better COP at winter

    What we do: we select for a DP of 4 to 5 and we can drop the HP as low as we want, the TEV will follow, winter and summer. Most of our packs are running this way.
    How can you do this? Is it with a variable speed compressor motor? Can you select the DP by adjusting the TEV?

    The theoretical maximum Carnot COP of a refrigeration system increases as the condenser temperature is reduced.

    I want to know if the COP of a real refrigeration system can be increased as much as the theoretical maximum Carnot COP change would indicate. For example, if the Carnot COP is doubled by reducing the condenser temperature, could a real system COP be doubled as well? Perhaps through the use of a variable speed compressor, and electronic expansion valve?

Similar Threads

  1. Operating Evaporative-Condensers in Extreme Winter Conditions.
    By stepperider in forum System Optimization
    Replies: 20
    Last Post: 29-07-2009, 09:35 PM
  2. heat load in winter
    By pramodpatil in forum Air Conditioning
    Replies: 12
    Last Post: 23-05-2009, 11:06 AM
  3. cooling tower winter operation
    By Lc_shi in forum Fundamentals
    Replies: 12
    Last Post: 14-04-2009, 02:59 AM
  4. Thermo King Winter Setting
    By Green Car in forum Trouble Shooting
    Replies: 0
    Last Post: 14-04-2009, 02:58 AM
  5. AC in the winter in wisconsin! will it work?
    By kurt854 in forum Air Conditioning
    Replies: 4
    Last Post: 13-06-2007, 06:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •