Re: walk in freezer smokey
If it is not a bad fan motor.........I hade one SMOKE last week; but you can smell that a MILE away!
a bad fan termination switch during defrost could cause the fans to run while the heaters are fired and would throw a MIST in the air.
Defrost cuts the fans and fires the heaters, then the other sensor senses that the coil is icing and then it turns the fans back on to ensure water wont be misted all over the box.
Check that out and maybe that could be it.