Results 1 to 10 of 10
    May 2010
    dalmacija
    11
    How calculate AHU performance?
    How can I manually from the known values of Return or Supply Air Volume, Return Air Supply Air readings and Readings
    calculate "AHU Performance Calculated "values (Total kW, kW Sensible, Latent kW, SHR, Condensate l / hr)
    As a here fridgetech.com/calculators/ahucalc.html
    Beginner in the world of air conditioners. Thank you all for your help.
    May 2008
    803
    10
    Re: How calculate AHU performance?
    if you have flash player, they have some simulators to play whit.
    have fun,
    http://www.techno-froid.com http://www.techno-froid.com/index.ph...d=31&Itemid=32
    Ice
    May 2010
    dalmacija
    11
    Thanks for your help, the best simulation yet on this topic. But how to calculate without a computer, only numbers, graphs, paper and pencil?
    May 2008
    803
    10
    yep, just like in the good old days.
    Ice
    Apr 2009
    Panacea, Florida
    81
    9
    Every air conditioning unit is different, and has unique values of output for the inputs you list. You therefore need to go to a manufacturer’s web site – Carrier, Trane, and York among others give free access to their performance data. Given a particular size and type of unit, say 5 ton, split air cooled air conditioner (as opposed to heat pump) you use the manufacturer’s performance tables to look up the total and sensible capacities, and total input KW.
    My book HVAC From Clean Sheet to Blueprint – A Mechanical Designer’s Guide to Design of Small Commercial and Institutional HVAC Systems describes how to use this data to select the air conditioner that matches your loads, and how to plot the data on a psychrometric chart. Once this is done, you can read the difference in specific humidity off the chart at the coil inlet and leaving conditions and compute the condensate removal rate.
    My book is currently available for free download at my HVAC design web site www.nettally.com/doughert.
    Sep 2010
    7
    Quote Originally Posted by jjosip View Post
    Measure the AHU inlet volumetric flow rate.
    Air inlet temperature and humidity
    Air outlet temperature and humidity
    Find out the barometric pressure.
    Using inlet temperature and barometric pressure calculate air density (kg/m^3).
    Multiply density by vol flow rate to get mass flow.
    Sensible (kW) duty is mass flow (kg/s) x temperature difference (K) x 1.006
    For latent, plot the inlet and outlet air conditions on a psychrometric chart and read the change in water content inlet to outlet (kg/kg), multiply this by air mass flow to get condensate rate (kg/s). To convert this to a latent duty you can read it from the psych chart or just multiply condensation rate by the latent heat of vaporisation (4.2 KJ/KgK)
    Sep 2010
    7
    Quote Originally Posted by Rich_J View Post
    Sorry, slight slip, 4.2 should be 2250KJ/KgK
    Is ther an edit function?
    Oct 2001
    Nottingham UK
    5,090
    42
    One of the Mods with Priviledges for the section can edit it for you.( Andy, Peter_1, Mark, chillin out, Brian_UK, WebRam )
    When you post a reply you normally get 15 minutes to carry out any editing - although since the forum upgrade this may have changed.
    I'm back on the Pale
    aalina387's Avatar
    aalina387 Guest
    Aug 2008
    OMAN
    40
    really valuable animations
  1. Suction gas <-> liquid line heat exchange and performance gains
    Last Post: 18-05-2010, 01:52 PM
  2. Need to warm a pond how to calculate it ?
    By Robert Nimni in forum Heat Pumps
    Last Post: 12-04-2010, 09:18 AM
  3. Replies: 3
    Last Post: 17-01-2009, 04:17 PM
  4. Formula to Calculate
    By suny in forum Fundamentals
    Last Post: 09-08-2007, 02:38 AM
  5. Low System Performance (Hunting ?)
    By rhlg in forum Technical Discussions
    Last Post: 25-10-2006, 01:05 AM