    Coldface panels



    Hi,

    Are there any experts on Elliwell Coldface panels out there?

    We have a 5 degree room with one of these and when it gets down to temperature, the evaporator fans stop. I want to keep the fans running to get air back to the probe and give a better indication of room temperature.

    What setting do I need to alter?

    I have been through the book and cannot find the right setting.



  2. #2
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Coldface panels

    i think you need to adjust setting fst, if the probe 2 (evap probe) reads higher than the set point of the room the fans will stop, try setting this setting to +20 and see if this helps

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Coldface panels

    Don't know whether this helps, but... see page 8

    http://www.frigo.info/content/file/COLDFACE_TEKNIK.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Coldface panels

    Nice link there Brian.
    Thanks Grizzly.

  5. #5
    Join Date
    May 2008
    Location
    UK
    Posts
    170
    Rep Power
    16

    Re: Coldface panels

    Thanks for your replies.

    Cool hibby, I looked at this setting but it doesn't make sense to me. Does evap probe mean air probe and if so then when room is down to temp it will read lower than the setpoint?

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Coldface panels

    wire the fans so they run all the time?
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Coldface panels

    Quote Originally Posted by R1976 View Post
    Thanks for your replies.

    Cool hibby, I looked at this setting but it doesn't make sense to me. Does evap probe mean air probe and if so then when room is down to temp it will read lower than the setpoint?
    Hi :
    it is a setting ment to "save" energy ,stops the evap fans when reach temp setting ,and yes as said before it could be changed go to their(eliwell) site
    http://www.eliwell.it/supportingdocuments.aspx?id=1506#
    and it should be easy enough to change.
    good luck
    Last edited by goshen; 03-09-2010 at 05:08 AM.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  8. #8
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Coldface panels

    Quote Originally Posted by R1976 View Post
    Thanks for your replies.

    Cool hibby, I looked at this setting but it doesn't make sense to me. Does evap probe mean air probe and if so then when room is down to temp it will read lower than the setpoint?
    hi, no evap probe is the evaporator probe (probe 2) also sometimes refered to as defrost termination probe, this will be monted either in the back of the cooler or strapped to the return bend on the end of the evaporator,
    if you set the setting to say -20 then it should keep your fans running all the time, but if your evaporator doesnt have fans and is off cycle only then short the fans to run all the time!!

  9. #9
    Join Date
    May 2008
    Location
    UK
    Posts
    170
    Rep Power
    16

    Re: Coldface panels

    Thanks,

    I now get the drift.

    We are using off cycle defrost at the minute so fans need to run in defrost, however, we are going to put electric defrost on soon so we will need to stop the fans on defrost eventually.

    Do you think stopping the fans on electric defrost, aids the defrost that much?

  10. #10
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: Coldface panels

    the fans stop on defrost anyway.the reason for the fan control is to stop the fans blowing warm air round the room after a defrost.personally i would not set the fst setting above 5 c

Similar Threads

  1. Dead load & live load for PU Panels
    By tjk2007 in forum Technical Discussions
    Replies: 5
    Last Post: 31-07-2009, 05:07 AM
  2. bubbles on insulated panels by start-up
    By klaverlover in forum Trouble Shooting
    Replies: 3
    Last Post: 05-09-2008, 06:57 AM
  3. Cold room panels
    By LLCooLJ in forum Commercial
    Replies: 6
    Last Post: 07-04-2008, 04:18 PM
  4. PUF panels Vs PIR panels
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 03-09-2007, 01:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •