    Daikin VRV central control



    Got another blinding one on the daikin VRV system ,it seems that the 2 units that cool the server room in this office set at (19oc) keep switching over to heat and ramping the temp up to 25oc .The cental controller for the building seems to switch them as it displays heat !!!
    Any ideas ???



  2. #2
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Daikin VRV central control

    Quote Originally Posted by Chillybilly View Post
    Got another blinding one on the daikin VRV system ,it seems that the 2 units that cool the server room in this office set at (19oc) keep switching over to heat and ramping the temp up to 25oc .The cental controller for the building seems to switch them as it displays heat !!!
    Any ideas ???

    A vrv in a server room..not recommended :-)

    What version of IManager do you have ?

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin VRV central control

    Sounds like you have heat mode set up in the daily schedules

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin VRV central control

    Quote Originally Posted by multisync View Post
    A vrv in a server room..not recommended :-)
    It amazes me as to the thinking behind the designers it must be the cost engineers who cross the splits off the list

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin VRV central control

    it may be a good idea to set the central controller up to NO CHANGE, this way if there is a schedule in place the set point or mode will not change.
    This unit should be locked into cooling and not auto mode.
    The other thing, for this to change over like this the indoor unit may be short cycling, like hitting a cabinet and recirculating the cold air over the return air sensor.
    Depending on what unit you have you may want to install a remote sensor to avoid this..

  6. #6
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: Daikin VRV central control

    Hey
    Set the indoor units up as cooling only or just delete these two addresses off the central controller. So they run independantly of central control. I am not that familiar with Daikin Kit. But this can be done on SANYO/TOSH/MITSU so I'd be amazed if Daikin don't have this function.

    I'm sure one of the Daikin Tekkies in here could help with either of these set up's

  7. #7
    Join Date
    May 2004
    Location
    Nottingham
    Posts
    5
    Rep Power
    0

    Re: Daikin VRV central control

    Interegated the controller yesterday ,dont know why they used VRV for the server room ,only angle i have is the rest of the building is VRV .

    Regards the controller and setup,the offending units are in cool only mode with a sp of 19oc ,they are not influenced by any time strategys in the controller so should not heat at all ,When the system does go into heat mode it does it without following any patterns ,eg one day in the morning the next day at dinner time .It logs no High temp alarms so i think it believes its doin the right thing ,all very odd ...............

    Might be the time to get the Daikin man in with his laptop and do a software upgrade ,the version in the controller at present is around 4 years old it seems ........Willpost the result

  8. #8
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin VRV central control

    Quote Originally Posted by Chillybilly View Post
    Interegated the controller yesterday ,dont know why they used VRV for the server room ,only angle i have is the rest of the building is VRV .

    Regards the controller and setup,the offending units are in cool only mode with a sp of 19oc ,they are not influenced by any time strategys in the controller so should not heat at all ,When the system does go into heat mode it does it without following any patterns ,eg one day in the morning the next day at dinner time .It logs no High temp alarms so i think it believes its doin the right thing ,all very odd ...............

    Might be the time to get the Daikin man in with his laptop and do a software upgrade ,the version in the controller at present is around 4 years old it seems ........Willpost the result
    I take you have an I touch controller and not the older type centralised contoller, what is the controller software version? This can be viewed in system - version information.

    You could also check:

    Verify 100% none of the start timers have been set with a target of ALL in schedules section.

    Could the units in question be part of a heat cool change over group? (check in change over settings section)

    Could the units be set up with Teperature limit settings?
    Last edited by VRVIII; 27-08-2010 at 05:56 PM.

  9. #9
    Join Date
    Sep 2010
    Location
    England
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV central control

    It is possible to have Comms room on VRV, Daikin now have a code you put in for comms room applications.

    I would personnally make sure the comms room units are in there own group, so make sure the schedules are not labelled ALL.

    You can also lock the controller into cool locally in setting 1B-002 then you have to press the 4 buttons for 5 secs.

    I would also prohibit any use of the local controller through the I-Touch.

  10. #10
    Join Date
    Sep 2010
    Location
    los angeles
    Age
    35
    Posts
    10
    Rep Power
    0

    Re: Daikin VRV central control

    Fresh air must also be supplied without increasing energy consumption and central management and control facilities have gained in importance, particularly for medium to large sized buildings.~

  11. #11
    Join Date
    Feb 2009
    Location
    england
    Posts
    22
    Rep Power
    0

    Re: Daikin VRV central control

    I have come accross a few lately were they run the vrv system in the day time for the comms room and turn them off at night and run the comms room on splits consultants love this idea (i dont mind it either if it gives me work)

  12. #12
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Daikin VRV central control

    is the system a three pipe or heatpump if two pipe heatpump system units will not cool if systm is in heating

  13. #13
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    20

    Re: Daikin VRV central control

    Quote Originally Posted by wardy2 View Post
    I have come accross a few lately were they run the vrv system in the day time for the comms room, and turn them off at night and run the comms room on splits.
    That is a way of dealing with the Comms Room wanting cooling all weekend/over night, while the offices are switched off. It would be worth giving Daikin all the info on this system in case the %load in the computer room is too small for the bigboy condenser.

    On a recent Mitsi system, the computer load was quite small in relation to the condenser, and having that comms room calling for cooling through the weekend (and overnight) while the rest of the system was off, gave problems for the compressor. We warned the customer (in writing) about the damage going on and offered a separate split or 2 for the computer room, but they would seemingly prefer to do the upgrade after they loose a compressor on the vrf. Up to them.

    If you have this kind of situation, it might be better to have a few offices kept running with the comms room to reduce the problem. But Daikin should be able to confirm whether it is an issue or not.

    As for designers choosing to include a comms room on a vrv/f system, I think they generally try to avoid this. But after handover, often a tenant moves in and builds a comms room under a general air-conditioner, or in a room intended as an office.

Similar Threads

  1. Daikin Super Inverter works like on/off control
    By 66sixty66six66 in forum Air Conditioning
    Replies: 4
    Last Post: 11-07-2010, 03:53 AM
  2. Replies: 2
    Last Post: 27-02-2010, 05:05 AM
  3. Daikin VRV hot start control
    By mchild in forum Air Conditioning
    Replies: 0
    Last Post: 04-06-2009, 03:15 PM
  4. Daikin control wiring
    By mchild in forum Air Conditioning
    Replies: 12
    Last Post: 24-11-2008, 12:38 PM
  5. Daikin A/C Cellar Temperature Control
    By Cellar Dweller in forum Fundamentals
    Replies: 15
    Last Post: 10-01-2008, 11:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •