    chiller pump problem



    I have a problem with a water chiller.
    The chiller is in the roof of the building
    and the water pump as well.
    When the pump is closed i have standing pressure 2 bar.
    When the pump starts working i have:

    suction water pressure 0 bar
    disharge water pressure 3.2 bar

    Why the suction pressure of the pump goes so down?
    I have problem with air coming in the circuit.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: chiller pump problem

    hi harry7 ,
    I take it you are monitering the water just before the pump + just after the pump? < are the gauges tested ? can you change them around ?<

  3. #3
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi sedgy.Thanks for the reply.
    The manometers are new!Before and after the pump.

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Harry 7,

    But the pump guarantees the circulation of water or not? Is it being a problem or just a curiosity?

    The problem (if there is any problem) could be the fact that with all water system off an equilibrium of the pressures is reached. When the water flows there is water pressure loss which will give to a decrease of pressure on the suction and an increase on the discharge. It is this difference caused by the pump who mantains the water in circulation. If you present any problems of cavitation try to pressurize your elastic expansion vessel if you have it. Check also if you don't have any excessive pressure loss on any accessory (dirty filters, pipe smashed, valve only partial open, etc.)...just ideas...
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi sandro baptista.The problem is that from the suction of the pump is getting air in the system through the mechanism[i do not know the word] which is getting the air out of the system!!!

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: chiller pump problem

    hi harry7,
    I am stuck on the word mechanism, ? flow switch?
    but running the c-water is important before running the chiller are there binda points you can moniter the water from ? are there air releafe valves that wil help you get the air out of the system ?

  7. #7
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Sedgy the mechanism i was refering is the air relief valve.
    {I couldn't remember the word in english}
    There are relief valves before an after the pump.
    When the pump starts working air is getting in the
    system through the air relief valve in suction side
    of the pump[0 bar}.
    When pump stops some air is getting out from the same relief valve.{2 bar}

  8. #8
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    yeah...exactly you mean air purger, right?
    Do you have expansion vessel of membrane type? I guess probably yes on some place...So pressurizing it a little more so you can get about 0,5 bar above the atmospheric pressure, so you will have a good tolerance I guess so it will never enters air again.
    To make progress is never good enough, I want to do better and better and better

  9. #9
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Yes sandro it is in the basement of the building.
    The pump is in the roof of building.
    There are 6 floors in the building.
    I have 2 bars in the pump when it is not working.
    Why should be fault in the expansion vesel?

  10. #10
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: chiller pump problem

    hi Harry, referring from your querries, it seems you don't have enough return pressure on the suction side of the pump that's why the pressure becomes slightly negative or vacuum. Have you tried adding more water in the circulating water system?.,if yes and still you have vacuum pressure in the return line then maybe you have a clogged return pipe line or a design issue.
    Regarding the 2 bars suction pressure when you stop the pump, i think your discharge check valve is not closing that's why the pressure is returning into the suction side of the pump and then increases to 2 bar.
    Some air relief valves have a built-in check valve to prevent air from coming into the mechanism and into the suction pipeline. In your case, you can temporarily replace the suction air relief valve with a good quality ball valve to prevent cavitation in your pump.
    hope this helps.
    <"No one is so smart, they just stay with problems longer and use their imagination">

  11. #11
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi ref!Thanks for the reply.I temporaly closed the ball valve under the releif valve.But the pump is pressing downwards and the releif valve is 1 meter higher from it.The pipe is about 10 cm thick.Could it be clogged?
    I increased the pressure from 1.5 bar to 2 bar in the roof from the water pressuse adjustment in the basement.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller pump problem

    Quote Originally Posted by HARRY 7 View Post
    I have a problem with a water chiller.
    The chiller is in the roof of the building
    and the water pump as well.
    When the pump is closed i have standing pressure 2 bar.
    When the pump starts working i have:

    suction water pressure 0 bar
    disharge water pressure 3.2 bar

    Why the suction pressure of the pump goes so down?
    I have problem with air coming in the circuit.
    Exactly where on water circuit did you measured that 2 bar standing pressure?
    What is pump make and model#?

  13. #13
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi nike thanks for the reply to.
    I measured the pressure before and after the pump.
    I do not know the model of the pump.
    It is covered with insulation.It begins with star delta.
    If that helps.

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller pump problem

    3,2 bar difference is to high for ordinary circular pump (canned rotor) usually used in such applications.
    That is head of 32 meter. We need to know what type of pump is in that chiller. Is it factory fitted or on place fitted pump.

    I increased the pressure from 1.5 bar to 2 bar in the roof from the water pressuse adjustment in the basement.
    If on the roof you have 2 bar than on lowest point in system you have 2bar + weight of water column (0,1 bar/m height diference) Your standing pressure at that point when water temperature is lowest possible must be pump pressure differential + height difference + cca. 1 bar to prevent air ingress and cavitation. Your expansion vessel pressure (before water pressurization) should be 0,1bar lower than that.

    Or follow this:
    Last edited by nike123; 25-08-2010 at 01:11 AM.

  15. #15
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Quote Originally Posted by HARRY 7 View Post
    Yes sandro it is in the basement of the building.
    The pump is in the roof of building.
    There are 6 floors in the building.
    I have 2 bars in the pump when it is not working.
    Why should be fault in the expansion vesel?
    If your circuit if full of water as it should be so you should have an expansion vessel because:

    - the water is cold the circuit is full » when water warm it will have an increase of specific volume which can burst the circuit

    - Or if the circuit was full of warm water when the water cools the opposite happens and it will happens a depressurization and the highest points will be at very low pressure and if you open the purge valve on this points air will enter. Also cavitation due to extremly low pressures if the water is not cold enough can result on cavitation that wears the pump and loses head.
    To make progress is never good enough, I want to do better and better and better

  16. #16
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    The pump is not factory fitted.
    There is an expansion vessel but it is in the basement of the building.Could it be that the problem because the pump is in the roof?But i have two bars in suction side before it starts working.

  17. #17
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Quote Originally Posted by HARRY 7 View Post
    There is an expansion vessel but it is in the basement of the building.Could it be that the problem because the pump is in the roof?
    No, no problem once you have that in count when you pressurize the expansion vessel.
    To make progress is never good enough, I want to do better and better and better

  18. #18
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Quote Originally Posted by HARRY 7 View Post
    But i have two bars in suction side before it starts working.
    I already give my opinion on a previous email. But another question: Does your expansion vessel is pressurized? When the pump start the decrease of the suction pressure is fast or takes times as the water temperature drop?
    To make progress is never good enough, I want to do better and better and better

  19. #19
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    As they told me from the phone the pressure drops very fast.
    I do not know if the vessel is pressurized.

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller pump problem

    Expansion vessel should be as close as possible to pump suction to maintain positive pressures throughout system.

    Last edited by nike123; 25-08-2010 at 12:48 AM.

  21. #21
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    So i have a problem nike?

  22. #22
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Of course it would be better to mount the expansion vessel at the suction of the pump to protect her better, but if the expansion vessel is in another place it keep to do its job allowing density flutuaction on the circuit.

    Look Harry if you want my advice: stop the pump and pressurize the expansion vessel membrane until you get 3,0 bar. It will be run good. Then send me feedback as soon as possible. You will be grateful. Can you do that? Also check the filter if it is clean.
    To make progress is never good enough, I want to do better and better and better

  23. #23
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Thanks sandro i will inform you about the results.

  24. #24
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Can you do it still in 1 hour so I can go to sleep after?
    To make progress is never good enough, I want to do better and better and better

  25. #25
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    I am at home ready to sleep.
    So good night!

  26. #26
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    OKAY Good night. Please don't forget to get out all the air that could exist on the system that will be concentrated on the highest points » where is the pump ready to sucked!!

    Good night
    To make progress is never good enough, I want to do better and better and better

  27. #27
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Hi Harry.

    Any news?
    To make progress is never good enough, I want to do better and better and better

  28. #28
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Look what i found.The pump still works
    the same suction 0 bar,discharge 3.2 bar.
    The expansion vessel which is in the basement of
    the building has 5 bar pressure and it is in the
    discharge part of the system.{discharge collecter}
    The pressure regulator is there to.{5 bar}
    Could it be this a problem for the system?
    The pump is a WILO.No other characteristics available.

  29. #29
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi sandro!How are you?

  30. #30
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Harry,

    What's the pressure now when the pump is stopped? It's very weird if also is the same. Something is wrong.

    I presume that the gauges are okay...and the stop valve that communicate the expansion vessel with the circuit is open, right?

    Do you "pumped" the expansion vessel membrane with more air as we talk about it?

    Also I don't see that the problem could be of the pump because the pump is doing its job circulating water, right?
    About the pressure regulator I can't also see right now the influence...but sure would be better if you can send us a water diagram.
    To make progress is never good enough, I want to do better and better and better

  31. #31
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller pump problem

    Quote Originally Posted by HARRY 7 View Post
    So i have a problem nike?
    Of course that you have, air is entering your system.

  32. #32
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller pump problem

    Quote Originally Posted by HARRY 7 View Post
    Look what i found.The pump still works
    the same suction 0 bar,discharge 3.2 bar.
    The expansion vessel which is in the basement of
    the building has 5 bar pressure and it is in the
    discharge part of the system.{discharge collecter}
    The pressure regulator is there to.{5 bar}
    Could it be this a problem for the system?
    The pump is a WILO.No other characteristics available.
    3,2 bar at pump discharge and 18 m height difference (about 6 floors) gives you exactly 5 bar pressure in basement. If other components of system could bare, raise pressure ( read in basement) to 6 bar (in expansion vessel air side and in instalation) and than check suction pressure at pump. If everything is same, than that pressure should be 1 bar.

    Although, it is strange to me that 32m head is at pump. If pump is capable of such high head than flow is minimal (highest head of pump is when there is no flow).

    Wilo BAC pumps (usually used in such application) have highest head of 25m (2,5 bar at 10-30m^3/h).
    Last edited by nike123; 26-08-2010 at 08:38 PM.

  33. #33
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Sandro,

    the pressure is two bar when the pump is stopped.
    the gauges are new,i did not pressure the vessel because i found 5 bar pressure in it.But i found it is on the discharge side of the pump,but in the basement.Is this a mistake?It is my first time on the circuit.I do not know how it worked last year.The pressure vessel communicates with the system.

    nike,

    i beleive i have minimal flow.but i have standing pressure 2 bar in the pump.why should i raise the pressure again?
    1 and a half bar before.
    maybe a restriction somewhere??

  34. #34
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Harry,

    If pressure the vessel as we talked you should have an increase of pressure on the pump discharge but also on its suction. The important is to run way from the zero bar at the suction of the pump. Don't forget after pressurize to purge the air on the highest point (p.e. on the suction)
    To make progress is never good enough, I want to do better and better and better

  35. #35
    Join Date
    Aug 2010
    Location
    US
    Age
    54
    Posts
    8
    Rep Power
    0

    Re: chiller pump problem

    May be chiller pump is undersized for the connected load.Youmay check it out proper condition.

  36. #36
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: chiller pump problem

    hi harry
    you ask why there is 5 bar on the discharge side on the ground floor when the pump is off, this is the HEAD pressure. keep the info comin we are all interested on the outcome , sedgy,

  37. #37
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: chiller pump problem

    Hi :
    we might be dealing with a water pump ,that has a negative npsh!!!
    or a clogged filter.you should use a negative manometer to messure this.
    regarding air relief valves ,we found that using one way relief valves, that close under vaccume, solves this problem,excpecially if the piping has crap..... insulation!!
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  38. #38
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Hi Harry.

    Any news?
    To make progress is never good enough, I want to do better and better and better

  39. #39
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi Sandro.I have not gone to the field again.
    I will inform you!

  40. #40
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    okay Harry. Have a nice weekend.
    To make progress is never good enough, I want to do better and better and better

  41. #41
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Have a nice weekend sandro.
    Good night from athens.

  42. #42
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    good night from Portugal. here still are 22:30
    To make progress is never good enough, I want to do better and better and better

  43. #43
    Join Date
    Mar 2008
    Location
    Romania
    Age
    43
    Posts
    44
    Rep Power
    0

    Re: chiller pump problem

    If the pump is working with 0 bar or negative pressure on the suction side it could cavitate and get damaged.
    I had the same situation on a 5 floors building and the only way to solve the problem was to rise the water pressure until, with the pump working, i read 0.5 bar on the suction side. The pressure in the basement was about 5.6 bars. Fortunately all the components were built to withstand that pressure.

  44. #44
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    ...Or we can the pump at lower level...
    To make progress is never good enough, I want to do better and better and better

  45. #45
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    I went to the field today.There is no water filter in
    the system.Nothing has changed in the pressures.
    It is a 30 years old water system.Could it be the system
    clogged somewhere?This is what i beleive.What is the next step?

  46. #46
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Have pressurize the expansion vessel membrane as I ask you to in a previous email?

    Stop the pump and you reach in both sides 2 bar (as you told me at you first post). Pressurize until you get 3,0 bar and see what you get at the suction when you run the pump.
    To make progress is never good enough, I want to do better and better and better

  47. #47
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi sandro!How are you?
    No i have not pressurise the vessel.
    So you tell me to pressurise the system to be 3 bar on the top or the vessel??

  48. #48
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Pressurize the expansion vessel membrane, please and the system will increase the pressure. Make sure the air is purged on the highest points and the system is full of glycol then the expansion vessel will done its job of compensate the volumetric thermal expansion.
    To make progress is never good enough, I want to do better and better and better

  49. #49
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: chiller pump problem

    Hi Harry how is the pump working now?

    Have you already rise the suction pressure of the pump?
    To make progress is never good enough, I want to do better and better and better

  50. #50
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: chiller pump problem

    Hi sandro.I have not gone to the field again.
    I will go next week.I will inform you!

Page 1 of 2 12 LastLast

Similar Threads

  1. ammonia pump problem
    By Sukhvinder in forum Industrial Compressors
    Replies: 10
    Last Post: 04-07-2010, 06:24 PM
  2. Problem with mc quay chiller.
    By HARRY 7 in forum Commercial
    Replies: 13
    Last Post: 14-05-2010, 09:35 PM
  3. Chiller problem
    By Dheeraj in forum Air Conditioning
    Replies: 4
    Last Post: 17-04-2010, 07:16 PM
  4. R11 Centrifugal Chiller Oil Problem
    By iceman007 in forum Trouble Shooting
    Replies: 8
    Last Post: 17-02-2008, 02:14 AM
  5. neslab chiller water pump problem
    By bill0577 in forum Trouble Shooting
    Replies: 5
    Last Post: 19-10-2006, 05:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •