Thread: Non contact thermometer
16-06-2005, 04:16 PM #1
Im curious if many of you consider non contact infared thermometer guns reliable for calculating superheat etc.
16-06-2005, 07:17 PM #2
Re: Non contact thermometer
NO,
If you look carefully' you will notice that the digits don't stop moving up and down one or two digits only but can be critical when it comes to superheat.
Chemi
16-06-2005, 08:56 PM #3
I agree chemi, I use IR thermometers all the time to obtain air off temperatures on our AC vents as the ceilings in my office block are 20 feet high. But I would never use it to obtain the discharge superheat on our chillers as the margine for error can be as much as 2 degrees which could prove criticle when callculating gas charges. dill.
18-06-2005, 03:29 AM #4
I have a fluke IR thermometer its handy some times for measuring air vent temps as dill has said but the area of view when the vent is 10 feet away is pretty wide (a couple of feet). I have used it a couple of times to measure discharge temps on compressors it works ok but you have to wrap the copper in black tape and hold the thermometer about an inch away otherwise it reflects and you get strange readings.
I normally use an ETI therma 1 with a 6 thermocouple switch box. A couple of minutes spent cable tying the beads to the important places allows you to check superheats really easily.
If I was doing preventative maintenance on large plant where I would be going back at regular intervals I would put matt black paint in places where I wanted to use the IR and possibly use it but for the most time its more of a cool toy than serious instrument
Laser Thermometer
By Kfoam in forum Tools and CalculatorsReplies: 24Last Post: 09-07-2007, 12:09 AM -
Samsung Contact Number
By Abe in forum Air ConditioningReplies: 2Last Post: 17-08-2006, 11:38 AM -
Infrared Thermometer
By Krups in forum Tools and CalculatorsReplies: 24Last Post: 29-12-2005, 07:55 PM -
Measure suction line pressure drop with thermometer
By Steve Wright in forum FundamentalsReplies: 7Last Post: 17-09-2005, 11:05 PM -
contact service probe
By Morph in forum Tools and CalculatorsReplies: 2Last Post: 09-04-2005, 08:22 PM