    Re: electrical current loads for copeland compressors

    Quote Originally Posted by JIMMY SMITH View Post
    what is the full load amperage of a copeland compressor model CRN5 0500 TF5 270
    LRA= 130A
    MCC= 30A
    RLA (Contactor sizing)= 21.4A
    RLA (Wire and breaker sizing)= 19,2A

    At 7,2°C/54,4°C 10K superheat = 17,7A
    At -6,7°C/48,9°C 20K superheat = 14,4A