    Question Inter-cooler valve sizing



    Hello Everyone

    I have a high stage -10°C open Intercooler vessel (A) supplied with liquid from the receiver. The sub-cooled liquid is then supplied to the -32°C surge vessel from where it is pumped to the evaporators. There are 2 low stage compressors -40/-10 which discharge into the Intercooler (A). I am upgrading the control valve on the liquid supply to the Intercooler and need to check the kW to size the valve correctly.

    My question is: Do I add the kW’s of the -32 system (evaporators fed from the -32 surge vessel) and the kW’s of the 2 -40/-10 compressors? Or is it a little more complicated than that?

    Any help greatly appreciated.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Inter-cooler valve sizing

    piewie ,
    I think you only need total of -10 compressors in KW as all flash gas from liquid line goes through these machines , as well as load from intercooler .
    Allow for minimun pressure drop you may get across valve so it can handle all conditions comfortably ie low head pressures in winter etc .
    A modulating valve would be the best option to smooth out loads on -10 compressors .

  3. #3
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: Inter-cooler valve sizing

    Thanks Ranger1 but I do not think that will answer the question as our -10 compressors are connected via a common suction to our other -10 surge vessel so the work being done by the -10 compressors comes from two separate sources. What about my original idea?

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Inter-cooler valve sizing

    Where does the -40 system get its subcooled or liquid make up liquid from ?

  5. #5
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: Inter-cooler valve sizing

    The -40 has a seperate surge which gets it’s liquid from the other -10 surge.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Inter-cooler valve sizing

    You have to determine loads from each -10 systems .
    Low side load has nothing to do with sizing of high side makeup valve .
    Work out maximum load compressor wise for each -10 & that will be your answer simply put .

  7. #7
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Inter-cooler valve sizing

    Make up liquid from HPR goes to intermediate pressure receiver(IPR). Portion of this liquid will flash. Second portion will subcool -32C liquid. Third portion will desuperheat hot gas of -40C compressors. Desuperheating and subcooling loads depend of total load(-32 or -40). For example. -32 load is 100 KW. 10% of this load or 10 KW is subcooling. The same approach is for desuperheating.

Similar Threads

  1. Replies: 3
    Last Post: 26-08-2009, 09:37 AM
  2. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  3. thermostatic expansion valve sizing
    By ank_gl in forum Air Conditioning
    Replies: 2
    Last Post: 03-03-2009, 04:22 PM
  4. expansion valve for CPU cooler
    By star882 in forum CPU Overclockers
    Replies: 0
    Last Post: 17-10-2006, 04:20 AM
  5. Carbo Cooler relief valve
    By flasah in forum NH3
    Replies: 2
    Last Post: 24-06-2006, 09:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •