    Hi,

    I am after some advice.


    I have a unit maneurope

    mtz 28 = 2.3hp

    mtz 36 = 3hp

    I have a 2.5mtr dairy case and some other company have just replaced old condensing units and put these on.

    they replaced 2 x aspera j2192gk

    now i have products freezing freezing back and the mtz 36 going out on internal kickson.

    I think they are oversized and the unit is short cyling on thermostat and not getting the core temp down just the air.

    any help please.

    cheers


    hello its me

  2. #2
    hbguy's Avatar
    hbguy Guest

    Re: oversizing

    There's short-cuts people will use in this situation but there will be no permanent solution other than replacing the units with the right size. Everything else (such as manipulating charge) is only treat symptoms, but you'll always have a problem.

  3. #3
    Join Date
    Feb 2004
    Location
    yorkshire
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: oversizing

    thanks i thought so too, thanks for getting back to me.

    cheers
    hello its me

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: oversizing

    Nearest i've found is NJ2192GK which is a low back pressure 1hp compressor. I'd say the replacements are slightly oversized...

    What were they thinking? Why did the two aspera comps die at the same time?

  5. #5
    Join Date
    Feb 2004
    Location
    yorkshire
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: oversizing

    the company that we do work for wants to be "green" so the fridge is a hussman and looks poor and the condensing units look in a shody state so they replaced these for these danfoss units that have maneroupes on instead of replaing the fridge. various problems as i shall list.

    !. too many amps burning plug out as it was wired to a 13a supply
    2. product freezing
    3. chiller too high on top shelf ( due to core temp not getting down to temp)
    4. frosting back
    5. v.low back pressure unable to change that with tev or gas charge.
    6. compressor not getting its cooling so going out on internal Klickson.

    this is in the first month that it was installed . v.poor.

    the whole chiller could be run off a 2hp condesing unit and 't' them together, with this company doing it i think its down to them.

    cheers
    hello its me

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: oversizing

    If it's going out on its internal clixon, then you have to measure only 2 things to find the cause: SH and AMP's.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. oversizing condenser fan motors?
    By delta T in forum Electrical
    Replies: 3
    Last Post: 14-07-2010, 04:58 AM
  2. oversizing condenser fan motors?
    By delta T in forum Chit Chat & Service Stories
    Replies: 5
    Last Post: 13-07-2010, 02:20 PM
  3. Oversizing Split A/C Inverters
    By back2space in forum Air Conditioning
    Replies: 10
    Last Post: 16-04-2009, 03:08 AM
  4. Oversizing EXV electronic expansion valve
    By aygul in forum Technical Discussions
    Replies: 5
    Last Post: 20-11-2003, 01:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •