Hi,
I am after some advice.
I have a unit maneurope
mtz 28 = 2.3hp
mtz 36 = 3hp
I have a 2.5mtr dairy case and some other company have just replaced old condensing units and put these on.
they replaced 2 x aspera j2192gk
now i have products freezing freezing back and the mtz 36 going out on internal kickson.
I think they are oversized and the unit is short cyling on thermostat and not getting the core temp down just the air.
any help please.
cheers
hello its me
-
21-08-2010, 08:41 PM #2
Re: oversizing
There's short-cuts people will use in this situation but there will be no permanent solution other than replacing the units with the right size. Everything else (such as manipulating charge) is only treat symptoms, but you'll always have a problem.
-
21-08-2010, 08:43 PM #3
Re: oversizing
thanks i thought so too, thanks for getting back to me.
cheershello its me
-
21-08-2010, 08:47 PM #4
Re: oversizing
Nearest i've found is NJ2192GK which is a low back pressure 1hp compressor. I'd say the replacements are slightly oversized...
What were they thinking? Why did the two aspera comps die at the same time?
-
21-08-2010, 11:02 PM #5
Re: oversizing
the company that we do work for wants to be "green" so the fridge is a hussman and looks poor and the condensing units look in a shody state so they replaced these for these danfoss units that have maneroupes on instead of replaing the fridge. various problems as i shall list.
!. too many amps burning plug out as it was wired to a 13a supply
2. product freezing
3. chiller too high on top shelf ( due to core temp not getting down to temp)
4. frosting back
5. v.low back pressure unable to change that with tev or gas charge.
6. compressor not getting its cooling so going out on internal Klickson.
this is in the first month that it was installed . v.poor.
the whole chiller could be run off a 2hp condesing unit and 't' them together, with this company doing it i think its down to them.
cheershello its me
-
22-08-2010, 08:42 AM #6
Re: oversizing
If it's going out on its internal clixon, then you have to measure only 2 things to find the cause: SH and AMP's.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
oversizing condenser fan motors?
By delta T in forum ElectricalReplies: 3Last Post: 14-07-2010, 04:58 AM -
oversizing condenser fan motors?
By delta T in forum Chit Chat & Service StoriesReplies: 5Last Post: 13-07-2010, 02:20 PM -
Oversizing Split A/C Inverters
By back2space in forum Air ConditioningReplies: 10Last Post: 16-04-2009, 03:08 AM -
Oversizing EXV electronic expansion valve
By aygul in forum Technical DiscussionsReplies: 5Last Post: 20-11-2003, 01:00 PM