    More leaks than a farmers market...



    Had a call to a new customer, 5hr 250 mile round trip, they were unimpressed with their local guy so i got recommended to them.

    The main problem was the wash system on the milk tank, these new ones need a wash program writing for them on a laptop if the default wash is not working out.
    It depends on the size of tank, 15,000L in this case and the water pressure etc how long fill times for the hot and cold water need to be etc.
    Spent three hours messing about getting it to work ok, and then they wanted a check over the fridge systems while i was there....

    Now i've seen bad brazing before, i've even been guilty of some if truth be told but i have never seen so many bad joints in such a short piece of pipe
    Thirteen joints in elbows and a tee as the suction lines exited the tank at the top, acces to this was from below 8ft up in the air with a gap 1ft wide between the tank and the plate heat ex and milk lines.
    All the brazing was full of bubbles/holes, one leaked so bad the leak spray wouldn't stay in it! i brazed over it all with some 15% rods and it turned out much better than i thought.
    Then i noticed another joint 9" up the suction line didn't look too clever either, on closer inspection the system had originally been installed using plumbing solder and all the heat i had put in had melted this joint too....

    The phials on the txv's were clamped over the fittings, i could poke a screwdriver between them and the pipe...

    After talking to the customer it turns out the original installers were lawn mower repair men, you couldn't make this stuff up

    Eleven hours on site, 10kg R22, other bits and pieces, be lucky to get any change out of a grand, moslty due to the poor work of the original installers.

    I'm doubtfull the new drop ins will be compatable with plumbing solder based on experience with R134a in the past so i think they will need to budget for new pipe work in the near future.

    Now finally to the question, is plumbing solder even legal for refrigeration service?

    Jon
    Last edited by monkey spanners; 21-08-2010 at 11:07 AM. Reason: speling



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: More leaks than a farmers market...

    Hi Jon.
    Amazing post as usual!
    It sound like technology has reached even Milk parlours now?

    I had heard that they were slightly more state of the art nowadays!
    Anyway I haven't time to check at the moment. (But I will!)
    I suspect either EN378 or The Pressure vessel Regs should cover brazed joints somewhere.
    (Where is our Legal Eagle Abe? Nowadays?)
    Cheers once again for the informative post.
    Grizzly

  3. #3
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: More leaks than a farmers market...

    I seem to recall that halocarbon refrigerants such as R134A are not compatible with tin/lead solder.
    But its common sense as you know not to use it.
    I will dig out my info and post the it ,as I have got it somewhere.

    Ps 250 mile drive and 11 hours that's what you call working for a living- what a star man

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: More leaks than a farmers market...

    Hi Jon,
    As we do exactly the same service, its like looking at mirror, can you take some photos?

  5. #5
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: More leaks than a farmers market...

    Are you talking about the tin/lead soft solder or the 2% 'yellow tip' rods that plumbers use for brazing (instead of the 15% 'brown tip' that we use)
    I've never ever seen tin/lead soft solder used in any system.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: More leaks than a farmers market...

    Thanks for the comments guys,

    Chemi, i'll take some pictures next time i go there, i nearly took a video with my phone but it was one of those when there was so much to do i just wanted to get on with it!

    Heres some vids from other farms i've installed/service,

    http://www.youtube.com/watch?v=hP0jnXT5SZI

    http://www.youtube.com/watch?v=Ipg1F...eature=related

    http://www.youtube.com/watch?v=v_w4NpE21ME


    Paul, yeah normal lead/tin solder!, they have used it on the discharge valve too as i could easily scratch it with a screwdriver.

    Not sure plumbers here use 2%, its either lead/tin or lead free for dinking water, but most likely it'll be plastic pipe now as its all they seem to fit!

    For general pipe jointing i use rothenberger rolot s2 which is 2% are these the 'yellow tip' ones you asked about?, for driers and sightglasses johnson mathey 5%, for txv's 15%, and for dissimilar metals i have some 38% either flux coated or some i dip in a pot of flux.

    Jon

  7. #7
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: More leaks than a farmers market...

    OK, I've pretty much only use 2 types, 15% for cu-cu, and 45% with flux for cu-brass, cu-steel etc.
    It's the way I was taught at school, and what every company I have worked for has done too.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: More leaks than a farmers market...

    Soft soldering in Europe not allowed

    EN378/2000 - 6.2.2.2.

    6.2.2.2 Soldering
    Soft soldering shall not be used for piping joints, the assembly of piping and where fittings are to be incorporated in
    the piping.
    NOTE: For such situations brazing or welding is preferable.

    6.2.2.3 Welding
    Welding shall comply with the appropriate European standards. When selecting the welding process, operating
    temperatures, materials to be jointed and composition of filler metal shall be considered.
    Fittings for butt welding shall be compatible with the piping material.
    Coated (e.g. galvanized) pipes shall not be welded, unless all coating has been completely removed from the joint
    area. Welded joints shall be suitably protected.
    Welders shall be in possession of a valid approval certificate for the work in accordance with EN 287-1.

    6.2.2.4 Brazing
    The compatibility of all materials including filler and flux with the refrigerant shall be thoroughly established by
    investigation. The possibility of corrosion shall be taken into account.
    Brazing shall not be used for ammonia piping, unless the material has been proved to be compatible.
    Brazing shall only be carried out by persons competent in this field.
    NOTE: Other non-detachable joints can be used considering that their suitability has been proved.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: More leaks than a farmers market...

    Paul, i think i'll try and get some 45% ones to see if they are better than the 38% ones wolseley group sell

    Peter, thankyou for the information, i'll let the customer know that their system has incorrect jointing materials used in it.
    Is it actually illegal or just not allowed but nobody official does anything about it?

    Jon

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: More leaks than a farmers market...

    Jon,

    It's forbidden according to EU directives where the UK has translated this to their own British standards.
    So, you have a written paper to show your client that the joints were made against the present law.

    But who will punish the initial installer? For that, you have to go to court or make an agreement with this installer (paying the cost to do it the proper pay)

    A good lesson for your customer: always work with qualified peoples who works according to proper/good craftsman rules.

    It's like driving too fast: if nobody complains or you're not catch, you can drive as fast as you like.
    Don't forget that you may not touch the work of someone else, otherwise you're loosing liability.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: More leaks than a farmers market...

    The standard quoted is only that a standard not a regulation although BS EN 378 2008 has replaced the the 2000 publication but the posted material is just the same.

    BS 7671 (17th edition regs) is only a standard but is used to enforce the law when things go wrong so ,as you already said if nobody does any thing about it.

    who is gonna care

    The Pressure equipment directive is a regulation in force in Europe which basically states the same information about compatibility.

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: More leaks than a farmers market...

    There are some small differences between the 2000 and 2008 version.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: More leaks than a farmers market...

    There is a large amount of change between 2000 and 2008 but I suppose its how you read it and which part.
    I was referring to the information you posted which virtually unchanged

Similar Threads

  1. Multiple leaks on capillary tube and suction lines
    By keepmecool in forum Domestic
    Replies: 30
    Last Post: 19-01-2010, 01:54 PM
  2. AC Market Segmentation - Where are VRFs?
    By nishant in forum Air Conditioning
    Replies: 3
    Last Post: 15-05-2009, 06:11 PM
  3. leaks in cars
    By coolhibby1875 in forum Chit Chat & Service Stories
    Replies: 2
    Last Post: 18-07-2008, 06:56 PM
  4. Replies: 10
    Last Post: 13-06-2008, 05:57 AM
  5. Leaks in refrigeration systems
    By Carlo Hansen in forum Fundamentals
    Replies: 3
    Last Post: 01-11-2005, 01:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •