20-08-2010, 09:11 PM #1
sanyo
what 1s a p 12 fault on a sanyo two way muli
-
20-08-2010, 09:28 PM #2
Re: sanyo
anybody has fault codes for sanyo? please help,i have a p-12 fault .
-
22-08-2010, 08:43 PM #3
Re: sanyo
Try this mate.
http://www.oceanairdist.co.uk/assets...lt%20codes.pdf
Cheers,
Andy.Health and safety first..........unless I'm in a hurry.
-
25-08-2010, 04:10 PM #4
Re: sanyo
SANYO model AY-X13CR
Know of where i can get grubby mits on manual?
many thanks
-
25-08-2010, 09:26 PM #5
Re: sanyo
have a look on here
http://www.heronridge.co.uk/tech_info.htm
-
01-09-2010, 01:46 PM #6
Re: sanyo
P12 is a indoor unit fan overload.
On a cassette on first commissioning check is the packing material is still inside the indoor unit
If this has been commissioned and has run for some time. Spin the fan by hand and switch on the remote controller. If the fan runs for a few minutes the PCB is faulty. If the fan does not run probably both fan motor and PCB need replacing (very unusual)Last edited by techguy; 01-09-2010 at 01:56 PM.
-
01-09-2010, 01:54 PM #7
Re: sanyo
Quite normal for the PCB to fail. Just changed eight of them on almost new units that have not been used for a period of time.
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.
-
09-09-2010, 09:42 PM #8
Re: sanyo
Indoor unit DC fan trouble
-
09-09-2010, 09:44 PM #9
Similar Threads
-
Sanyo technical number needed
By marc5180 in forum Air ConditioningReplies: 6Last Post: 17-08-2010, 07:05 PM -
Sanyo anytime online training and stuff
By King of VRF in forum Air ConditioningReplies: 2Last Post: 02-02-2010, 06:21 AM -
Sanyo fault codes
By Slim R410a in forum Air ConditioningReplies: 3Last Post: 03-11-2008, 08:02 PM -
Sanyo system needs supplemental heat
By mchild in forum Air ConditioningReplies: 2Last Post: 29-11-2007, 02:50 PM -
fault on a sanyo unit
By marc5180 in forum Air ConditioningReplies: 7Last Post: 18-08-2007, 11:04 PM