    heat coefficients formula .



    Hello

    Please can some one translate me this heat coefficients formula .

    Assume a heat exchanger is rated at 1000 Btu/hour ft oF how many latent heat is capable to move per hour ??

    I can not understand why there is the F (Fahrenheit) in the formula ???

    Thanks
    Marco EU



  2. #2
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: heat coefficients formula .

    From convective heat exchange:

    Q = U A deltaT

    Where: Q is heat transferred, BTU/hr.
    A is heat transfer area; Sq Ft
    DeltaT is the prevailing temperature difference:

    May be the log mean Temp Diff or may be local Temp Difff; with Latent Heat Exchanger and low pressure differences the average calculates the same as log mean...

    U is heat transmission coefficient: Nominally has units for entire exchanger of BTU/hour/ft^2/Def F. BUT

    If you are evaluating something like a single heat exchanger tube; or a tube in tube heat exchanger; the object is to establish the Length of the heat exchanger required.....so you will end up with Heat; per unit length; per unit temperature difference and the HT area, per unit length, is developed within the 1000 number.

    Insulation effectiveness also expressed without the area term as you are trying to arrive at an effective thickness...But your number well out of range for reasonable insulation performance.

    Once you have the Q for the heat exchanger, the mass flow for the latent fluid, presuming constant pressure, is the Total Heat Exchanged divided by the Latent Heat of the refrigerant at that temperature.

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  4. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  5. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •