Results 1 to 3 of 3
  1. #1
    Join Date
    May 2010
    Location
    Malaysia
    Posts
    12
    Rep Power
    0
    Expansion valve bulb & capillary tube
    Hello there,
    Our refrigeration system has being fitted with TEV Sporlan DAE 10, 15 & 20. And we had a problem with the sensing bulb & capillary tube was from copper materials & being coated with nickle or tin , after about 2 years in operation the sensing bulb & capillary tube which made of cooper was having badly damage by corrosions (direct Or indirectly with Ammonia from the system).
    I'll being inform even the Danfoss TXV's for model TEA, TEAT bulb and tube are copper and cap is steel. And whole are nickle coated.
    Anybody the same experience to be share or any suggestion for the replacement ?????
    Tq
  2. #2
    Join Date
    Oct 2010
    Location
    Monterrey, Mexico
    Age
    47
    Posts
    13
    Rep Power
    0
    Re: Expansion valve bulb & capillary tube
    you can try with Mycom Mayekawa are specialist on NH3, the valve must be all stell.
  3. #3
    Join Date
    Oct 2010
    Location
    Monterrey, Mexico
    Age
    47
    Posts
    13
    Rep Power
    0
    Quote Originally Posted by Paco villarreal View Post
    sorry steel....
Similar Threads
  1. Expansion noise - capillary tube into evaporator
    By desA in forum Fundamentals
    Last Post: 07-02-2010, 05:26 PM
  2. Fixed orfice tube x expansion valve
    By Acrisoft in forum Air Conditioning
    Last Post: 06-09-2009, 02:07 PM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Last Post: 10-03-2009, 01:03 PM
  4. Benji
    By benji in forum Trouble Shooting
    Last Post: 30-01-2008, 01:25 PM
  5. metric capillary tube
    By tralex in forum Fundamentals
    Last Post: 21-02-2006, 06:57 AM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts