    Diagnosing Daikin problem



    FTXD50JVEA / RXD50JVEA.

    Won't run. H6 fault code. No residual output current from compressor, which u would expect even if at fault.

    Daikin say replace PCB, compressor and fan.

    Is it possible to diagnose more accurately, as customer rightly points out, thats like your garage telling u to replace the engine, gearbox and wiring loom and that will fix your car. So would buying a new one.

    Daikin adamant that all three components must be replaced, but interestingly customer had a similar problem just before the warranty expired, and only the PCB was replaced.

    Any assistance / comments appreciated.

    AJ



  2. #2
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Diagnosing Daikin problem

    I would go with a new unit which will offer 5 years warranty with not much more outlay..

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Diagnosing Daikin problem

    Replace the unit.
    It's like $650 just for both outdoor PCBs. Not worth fixing daikin when they are out of warranty, parts are too pricey.
    Get a panasonic if you want something more reliable, or a fujitsu if you care about cheap parts 5 yrs from now.

  4. #4
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: Diagnosing Daikin problem

    Changing all parts seems like poor advice to me from a manufacturer. Compressor, fan and PCB can all be checked for correct operation.

    The fan motor will be a simple resistance test, PCB can be checked for correct output, compressor can be judged easily enough. Download the manual and follow the steps for H6, im sure you will work it out.
    Last edited by Mentallist; 06-09-2010 at 10:31 PM.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. problem with DAIKIN FCQ 71 > i need technical book
    By mimifrigo in forum Air Conditioning
    Replies: 7
    Last Post: 13-01-2010, 03:06 PM
  3. DAIKIN problem
    By mimifrigo in forum Air Conditioning
    Replies: 3
    Last Post: 05-01-2010, 09:02 PM
  4. Problem with an inverter compressor in V.R.V system DAIKIN R 407
    By Harris Greece in forum Air Conditioning
    Replies: 10
    Last Post: 24-11-2007, 12:53 AM
  5. DAIKIN problem ?
    By AaronX in forum Air Conditioning
    Replies: 11
    Last Post: 12-10-2007, 02:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •